Realistically if you are looking at just a switch and maybe a small defrost heater then 1A / 230V is enough and you could use 2.5mm 2-core SWA with an RCD for supply disconnection (as it would fail on the typical min 6A OCPD for domestic style boards). If the house is PME supply and you are looking at outdoor stuff you might even want to make this a TT arrangement.

Using transformers for lower drop as @James suggests is possible, but I would suggest unnecessary complexity if you don't really need it.

Cable works out at about £1/m plus VAT.:

You can either use SWA network cable and both can be buried directly in the ground but I would strongly advice using some twinwall duct for both power and fibre and you can use any outdoor style fibre that is strong enough to be pulled through. Mains SWA is safe enough beside even normal copper network cable as it has an earthed screen in the form of the armour. This is the sort of thing (but shop around, this was just my first result that was what I was trying to illustrate) so around £1.60 per meter plus VAT:

Typically you would want an access chamber around every 200m to allow cable pulling and potentially to allow a section to be repaired. It also allows you to have one run out and then split at the box to serve other end points.

BT/Openreach typically use this system for pavements or footpaths (not on a road where heavy concrete or cast iron cover and a concrete or brick box is then needed for the loading):

However, you can see that a complete box (say 4 * stacked sections to get 60cm depth, and lid) you are looking at around £600 per box.

So for 600m run you are looking at around 4 grand for duct, 3 boxs, and SWA cable delivering 1A power (before you add fibre and network switch). However, if fibre is needed out there then most of that cost is going to apply anyway.
 
Last edited:
Also, is it bad to go direct from point A to point B if it involves crossing a field which may have LGVs crossing for event setup and take-down, should the trench go around the perimeter?
If the cable or duct is buried deep enough (say 0.4-0.5m below surface) then it is not important. However, if the field is ever used for agriculture then you really need around 1-1.2m depth.

If this was a permanent system then you might want it routed around the edge of fields to allow for future changes in land use (e.g. adding building) without having to change this, however, that might not be an issue for the owner here.
 
Realistically if you are looking at just a switch and maybe a small defrost heater then 1A / 230V is enough and you could use 2.5mm 2-core SWA with an RCD for supply disconnection (as it would fail on the typical min 6A OCPD for domestic style boards). If the house is PME supply and you are looking at outdoor stuff you might even want to make this a TT arrangement.

Using transformers for lower drop as @James suggests is possible, but I would suggest unnecessary complexity if you don't really need it.

Cable works out at about £1/m plus VAT.:

You can either use SWA network cable and both can be buried directly in the ground but I would strongly advice using some twinwall duct for both power and fibre and you can use any outdoor style fibre that is strong enough to be pulled through. Mains SWA is safe enough beside even normal copper network cable as it has an earthed screen in the form of the armour. This is the sort of thing (but shop around, this was just my first result that was what I was trying to illustrate) so around £1.60 per meter plus VAT:

Typically you would want an access chamber around every 200m to allow cable pulling and potentially to allow a section to be repaired. It also allows you to have one run out and then split at the box to serve other end points.

BT/Openreach typically use this system for pavements or footpaths (not on a road where heavy concrete or cast iron cover and a concrete or brick box is then needed for the loading):

However, you can see that a complete box (say 4 * stacked sections to get 60cm depth, and lid) you are looking at around £600 per box.

So for 600m run you are looking at around 4 grand for duct, 3 boxs, and SWA cable delivering 1A power (before you add fibre and network switch). However, if fibre is needed out there then most of that cost is going to apply anyway.
Thanks for the detailed analysis. much appreciated. :)
 
If the cable or duct is buried deep enough (say 0.4-0.5m below surface) then it is not important. However, if the field is ever used for agriculture then you really need around 1-1.2m depth.

If this was a permanent system then you might want it routed around the edge of fields to allow for future changes in land use (e.g. adding building) without having to change this, however, that might not be an issue for the owner here.
It's parkland so no agri involved, but always best to plan for the unexpected!
 
Realistically if you are looking at just a switch and maybe a small defrost heater then 1A / 230V is enough and you could use 2.5mm 2-core SWA with an RCD for supply disconnection (as it would fail on the typical min 6A OCPD for domestic style boards).
Looking at the 2-core SWA cable, for 1.5mm the armour is lower R than the conductor!

But for 2.5mm considered by myself the R1 = 7.41 mOhm/m and R2 = 8.8 mOhm/m, so R1+R2 totals around 9.8 for 600m, say Zs approx 11 ohms allowing for TN-S supply.

That would meet disconnection on a 3A FCU as Table 41.4 has Zs for a 3A BS 1362 fuse as 22 ohms. It still needs RCD protection, but it is always nicer to know you can safely disconnect on the OCPD!
 
That would meet disconnection on a 3A FCU as Table 41.4 has Zs for a 3A BS 1362 fuse as 22 ohms. It still needs RCD protection, but it is always nicer to know you can safely disconnect on the OCPD!
That was 5s as a sub-main. Probably it would be considered a final circuit where it is Table 41.2 for 0.4s disconnection and then a max Zs of 15.6 ohms for 3A fuse, so still OK.

While they oly give 3A and 13A in that table, you can also get smaller fuses (1A & 2A) but for typical network switch with switch-mode PSU you run the risk of switch-on surge weakening or taking out too small a fuse.
 
That was 5s as a sub-main. Probably it would be considered a final circuit where it is Table 41.2 for 0.4s disconnection and then a max Zs of 15.6 ohms for 3A fuse, so still OK.

While they oly give 3A and 13A in that table, you can also get smaller fuses (1A & 2A) but for typical network switch with switch-mode PSU you run the risk of switch-on surge weakening or taking out too small a fuse.
@pc1966 Are you purposefully not taking volt drop into account? If so, may I ask please what your reasoning is behind this?
 

Reply to What type and size of cable for a long underground run in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm going to be wiring up my garden office with power and ethernet underground and I need advice on the best way to run the cables as I have...
Replies
18
Views
2K
Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
Replies
9
Views
1K
I am an enthusiastic retired engineer rebuilding a barn in France from scratch and am having problems sizing my incoming electrical cables. I have...
Replies
6
Views
2K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
1K
OK. I can already feel the eyes rolling I am working in a yard where we are having trouble with vandalism. There is absolutely no way of getting...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock