well doesn't that circuit need to be protected like all the other circuits which are all rcbos so I thought it would be best for this to be a rcbo instead of a 3P+N MCB with a RCD. But am I right to use a 3P+N breaker for 3 phase though ?
only need an RCD device if you are supplying the equipment through a socket. Otherwise it's just a triple pole mcb and neutral isn't switched.
 
So guys , for example supply to 3phase roller shutter door motor with attached 1m lead , if socket was high level ( say 3.5m up ) controlled by low level isolator, would you still put it through an rcd ?
 
So guys , for example supply to 3phase roller shutter door motor with attached 1m lead , if socket was high level ( say 3.5m up ) controlled by low level isolator, would you still put it through an rcd ?

There is no exception for height or accessibility in the regulations.

The designer of the installation may do a risk assessment to justify not providing RCD protection if there is some reason why RCD protection may be undesirable.
 
You will need to now if there is start up current on the equipment. To choose what type of mcb / rcbo B C or D .Also Just wondering if 16amp ocpd is a bit close to the limit if the equipment demand load is also 16amps.
 

Reply to What type of circuit breaker would be used for a three phase circuit? in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Hi, I'm doing my Level 3 Electrical Install course, and I'm doing distance learning so most of the work is being done by myself with no guidance...
Replies
0
Views
304
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
862
Hi there currently doing some diversity calcs for college work and had a query about what diversity factor to apply to a 16A 3 phase commercial...
Replies
3
Views
1K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
678
I live in Thailand and my home has 240v, 3 phase power supply. I want to add an electric car charger but first want to determine what the outlet...
Replies
0
Views
672

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock