I have just finised an EICR on a new extension. The previous electrician cannot be contacted.

The work was pretty shoddy. No identification sleeving on cables where needed including some earths. The 3 possible codes are as follows:

1. 1mm line conductor in the 6A MCB was loose due to being in with a 1.5mm and also 2.5mm conductor. I have made sure the termination is now tight but I really dont like the thought of 3 differing size conductors in the same MCB. I never do this as it is likely the smallest one will at some point not be well terminated. ?C2

2. Single socket for the fridge hidden in cupboard next to fridge, which is fine, however it is attached to the really flimsy wobbly bit of board on the back of the units. (You know the stuff, more like cardboard than wood). It is already loose. ?C2

3. Integrated LED downlights completely covered in insulation. Im not sure about this one. Its shoddy, but as they are integrated the lamp cannot be changed for a halogen so perhaps a C3 or no code? It would be a C2 if not integrated.

Cheers all.
 
Evening all.

I have just finised an EICR on a new extension. The previous electrician cannot be contacted.

The work was pretty shoddy. No identification sleeving on cables where needed including some earths. The 3 possible codes are as follows:

1. 1mm line conductor in the 6A MCB was loose due to being in with a 1.5mm and also 2.5mm conductor. I have made sure the termination is now tight but I really dont like the thought of 3 differing size conductors in the same MCB. I never do this as it is likely the smallest one will at some point not be well terminated. ?C2

2. Single socket for the fridge hidden in cupboard next to fridge, which is fine, however it is attached to the really flimsy wobbly bit of board on the back of the units. (You know the stuff, more like cardboard than wood). It is already loose. ?C2

3. Integrated LED downlights completely covered in insulation. Im not sure about this one. Its shoddy, but as they are integrated the lamp cannot be changed for a halogen so perhaps a C3 or no code? It would be a C2 if not integrated.

Cheers all.
In response to above...
1) I’m not a fan of multiple circuits in an mcb, do you know what they are feeding? , I would double over 1mm and make sure they are all secure as you said you’ve done, put it down as C3 recommending circuits be split on to separate mcbs

2)C3 unless it’s getting used to plug and unplug regularly

3)If they are led a C3, halogens then there’s a greater risk of fire so C2
 
do you think an "electrician" would have put 3 different sized cables in 1 mcb?.... its all to common for the original "electrician" to be un contactable... usually the homeowner or builder!
 
1. two sizes is bad enough but three?
The loose connection would be a C2 I feel but as it was resolved at the time then just a recommendation to at least have the same size conductors (why does any one want 2.5mm² on a 6A MCB in a domestic residence).
2. Not likely to be disturbed another comment on poor insulation and recommendation for support of the socket.
3. C3 risk of failure of the fitting, not overly likely to cause fire as the fitting will overheat and fail first (probably!)

If that is all you have to code then it is in a good state!
 
Most common things I find are
Lack of circuit chart information and circuits vulnerable to testing.
Poor inadequate labelling of circuits
No label for mixed wiring
No safety electrical connection on earth clamps
No rcd test labels
 
No codes on any!
Yes you are being overcautious, its an eicr not eic so your there to test its safe not to sign it off as your own, nothing wrong with recommendations but to give and installation an unsatisfactory for theese minor issues would be incorrect imo.
 

Reply to What would you code these as? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Doing an inspection and came across this. Feeds are as follows: Cutout to Meter - 25mm Meter to connector blocks - 25mm Connector blocks to...
Replies
64
Views
5K
Another what code! This is in conjunction with an EICR I have just carried out. 9.5kW shower on 6mm and 32A MCB. Been in place for a long time...
Replies
8
Views
3K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
Afternoon all, A quick EICR question. I have found a Ring Final Circuit that has been run in 1.5/1mm twin and earth. It is RCD protected and OCPD...
Replies
24
Views
4K
Hi Im newto this forum and hello to everybody. Im experienced electrician with 15 years of experience in all kind of domestic premised. Some...
Replies
42
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock