Discuss When electrics go wrong!!! in the UK Electrical Forum area at ElectriciansForums.net

Got a call out yesterday afternoon. Told electrics had tripped, turned back on and keeps tripping every few minutes so could I come and check as had no power to sockets, kitchen and half the house.

Arrived to find the following:

95F591D5-0ADF-44D3-9260-4482BB9580F2.jpeg
1E579835-39E6-4EA0-8905-E83F0A81DC28.jpeg
6EE183AD-F973-4447-AEC8-6A8E29CF3D32.jpeg


Basically the far right breaker was a 50A supply to a second DB for one half of the house (big old farmhouse) which includes a 10.5kw shower, sockets, immersion and lights. Also 2 x 32a socket circuits (one of which was the kitchen) a 20a socket circuit and 16a second immersion.

All hanging off a 63a RCD and the board had never been checked in the 18yrs since it was installed.

So I managed to give them some power back. But told them they need a new board now asap and a full EICR doing, as I wouldn’t change a board without doing it anyway (especially not on house where I’ve been called to a melted board) and investigation was needed to check why that 50A breaker had obviously also overheating given the melted plastic around the busbar connection.
 
The Berlin Wall fell in ‘89 I think… all thanks to knight Rider himself, David Hasselhoff.
One of my regrets was not going to the Pink Floyd concert in Berlin to mark that.

There was a minibus going from Dundee arranged by Groucho's (closed now, was 2nd hand record shop and outlet for local gig tickets) but various friend could'nd be bothered and I gave up on the idea.
 
One of my regrets was not going to the Pink Floyd concert in Berlin to mark that.

There was a minibus going from Dundee arranged by Groucho's (closed now, was 2nd hand record shop and outlet for local gig tickets) but various friend could'nd be bothered and I gave up on the idea.

You'd need to go for a week just to listen to one Pink Floyd song though!!
 
I remember groucho’s!

The nightlife was varied when I lived up there.
No1’s, Deacon Brodies, O’Neills… student union, of course.
Mardi gras, fat sams, de’stihls….

That all stopped when we moved to the posh end of Carnoustie
 

Reply to When electrics go wrong!!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
A bit of a mini essay but these questions have been building up in my mind over the last weeks and months as I've been studying and volunteering...
Replies
6
Views
3K
Hi everyone, Lets get the s#1t stirring out of the way straight up... Yes I'm a sparkie, and a good one, but for all you Brits, I was trained...
Replies
8
Views
5K
V
And the importance of being able to read them. This is a subject that really concerns me with the apprentices where I work and the management...
Replies
36
Views
13K
cranedude
C
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
77K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top