th_walking_dude

Hi All

Hoping one of you kind people could give me a few pointers with a job I am going to look at next week.

It's basically fault finding on an intercom system, a tenant in an apartment can't hear when people are buzzing up to them, that's about all I know so far.

I'm afraid to say I don't know much about intercom systems, the job is part of a maintenance contract I have with a property management company so it's not really something I can easily avoid and to be honest as it's a weakness I would rather get stuck in, get good at it and make it a strength but ideally without making a fool of myself in the process!!!

Having lived in an apartment myself I know how crap handsets can be so it is quite likely a dud handset but it would go against the grain to go around blindly changing parts without knowing why.

So if any one has any faultfinding tips or hints would be really appreciated.

Can't find any good resources online.

Also I don't suppose there are really any books which touch on this too much but if anyone could recommend anything that would be great.
 
Don't have a great deal of experience with these things but surely the place to start would be belling out the cables from the door to the flat in question.
Eliminate things one by one and what you're left with has to be where the problem lies
 
And corrosion and weakness on the contacts. The cable is easily snapped.

PS , check the transformer output if the fualty one is on the long run.
 
And corrosion and weakness on the contacts. The cable is easily snapped.

PS , check the transformer output if the fualty one is on the long run.

I like the transformer idea, that would be fairly straight forward. If there's a break in continuity that sounds like it is going to be a pig! I wish I knew what handset it was so I could swap that over first to rule that out. I'm probably making a mountain out of a molehill in my head about this but I don't like not knowing what I'm doing, Thanks for your advice so far gents.
 
If it's not ringing the phone in the flat, the 1st thing I would check would be the button for that particular flat whilst checking for loose broken contacts.

Thank you, the button was what I thought about when the lady was telling me about it. Are these generally interchangeable parts or would you swap the panel over? Thanks to the wonders of google maps I can see the panel is only small, maybe 5 or 6 buttons on it and the flat number is low so probably ground floor and hopefully near the panel!
 
I know your right, just have to start with what I know for sure and fill in the blanks! best way to learn that's for sure.

I haven't fitted loads of them, but when I put them in small blocks of new build flats I'm doing I use a make called bell systems

probably a far cry from the best but all the parts are changeable speech unit, buttons, etc. They are also easy to fit.
 

Attachments

  • image.jpg
    41.4 KB · Views: 118
I haven't fitted loads of them, but when I put them in small blocks of new build flats I'm doing I use a make called bell systems

probably a far cry from the best but all the parts are changeable speech unit, buttons, etc. They are also easy to fit.

That's awesome you've (all) been a massive help. I have seen those online. sods law they have an install from the 90s and I won't be able to get parts although having looked at those systems I don't imagine changing the whole panel wouldn't be too terrible.
 
I have some spare time tomorrow so spend a bit of it looking at those Bell manuals, should give me a solid understanding of how they work, even if it's not a Bell brand I'm sure it will be a similar set up.

Thanks again :)
 
That's awesome you've (all) been a massive help. I have seen those online. sods law they have an install from the 90s and I won't be able to get parts although having looked at those systems I don't imagine changing the whole panel wouldn't be too terrible.
As recent as the 90s... You will be doing well!
some of the older ones have some weird and wonderful methods of operation.
start at the panel to check the push.
If it's not right short across the push to make double sure.
if ok check the handset
watch out for common wires that are sometimes looped from flat to flat
the likes of videx and bpt have tech support who are quite good tbh.
check out intercomsrus who have an excellent handset finder bit on their site which has got me out of a spot on a few occasions
the hardest part of fixing a door entry is getting the full picture about what the problem is
is everyone else's working ? Oh yeah. Then after you've spent a bit getting a handset and the like the neighbour says his isn't working either and it's the lock that's faulty!
you get the drift I'm sure
 
Just a quick update, went to this job the buzzer was working when calling the effected flat but not ringing the phone upstairs so, either a lose connection, dodgy handset or break in continuity I thought. Opened up the handset checked all was ok and from what I could see it was, closed it back up and went downstairs to have a look in the control panel but thought I'd try the buzzer again and it worked right away, tried it a few times and it was fine. I asked the tenant if it was an intermittent fault and he said it has never worked, not even once so it looks like a loose connection in the handset (i did tighten them) or a break in a wire in the handset that is now sitting pretty. Either way the jobs a good un (for now at least!)

Just wanted to post an update and say thanks for everyones help and advice, I spent a few hours reading up on these and looking at wiring diagrams so feel a lot more comfortable doing these in future.
 
Just a quick update, went to this job the buzzer was working when calling the effected flat but not ringing the phone upstairs so, either a lose connection, dodgy handset or break in continuity I thought. Opened up the handset checked all was ok and from what I could see it was, closed it back up and went downstairs to have a look in the control panel but thought I'd try the buzzer again and it worked right away, tried it a few times and it was fine. I asked the tenant if it was an intermittent fault and he said it has never worked, not even once so it looks like a loose connection in the handset (i did tighten them) or a break in a wire in the handset that is now sitting pretty. Either way the jobs a good un (for now at least!)

Just wanted to post an update and say thanks for everyones help and advice, I spent a few hours reading up on these and looking at wiring diagrams so feel a lot more comfortable doing these in future.

Nice for someone to actually come back and give the result , and a thank you at the same time.

Well done for that.:smile:
 

Reply to Where to start? Intercom fault finding. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening all, I had a quick Friday afternoon domestic job that has turned into a PITA and I'd appreciate your help. While adding some new lights...
Replies
10
Views
869
Hi I'm trying to find if I have a fault in these to brakers of in the lines. The 32A braker leads as far as I know only to a junction box that use...
Replies
18
Views
1K
The big stately home I’ve been working in has an EMS 5096 alarm system with over 100 detectors and 3 (that I know of) panels. All detectors are...
Replies
19
Views
973
Hi all I don't appear to be able to post in the DIY forum so apologies if this is the wrong place. I live in a block of flats with an external...
Replies
3
Views
839
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
551

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock