Search the forum,

Discuss Who does just a Zs when carrying out a periodic on a lighting circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Im all for health and safety but come on where has the common sence gone ,lets all run out and do a dead Ze test , oh yes by enquiry , how are they going to know what it is, bad enough trying to get them to reseal a meter !!!
 
I've just been testing a hotel. Not possible to shut whole DB's down so I use the R2 wander lead method to make sure lights, accessories etc have an earth connection. It hasn't been possible to connect the wander lead directly to the earth point at all the DB's due to being a tripping hazard and too many doors to take it through. so I connect to earth on the nearest socket using a breakout box. Obviously I ensure there is an earth at this point, then I go round with the wander lead and make sure I get a reading, then carry out my Zs testing later. I wasn't happy doing it this way since the last 3 PIR's carried out at this hotel had R1+R2 readings recorded in the schedules of test results, however, doing it this way I found over 10 metal light fittings that had no earth connection. Obviously I felt much better about my chosen option and I had agreed it with the client beforehand and duly noted it down in the limitations box. Obviously the previous jokers just took one R1+R2 and Zs reading per circuit.
 
Im all for health and safety but come on where has the common sence gone ,lets all run out and do a dead Ze test , oh yes by enquiry , how are they going to know what it is, bad enough trying to get them to reseal a meter !!!

I've done live testing (including Zs) on every NICEIC and ECA technical assessment that I've ever done (a few) all without any comment from the assessor.

The NICEIC official line stems from the EAWR 1989 and the lack of distinguishing between 'working live' and testing.
 
It is acceptable to just put a tick in the box for R1+R2 or R2 on a PIR, but not on an EIC. But if you are measuring or confirming then you may as well put down the recorded result anyway, this will give you something to work with next time around.

Cheers.........Howard
 
It is acceptable to just put a tick in the box for R1+R2 or R2 on a PIR, but not on an EIC. But if you are measuring or confirming then you may as well put down the recorded result anyway, this will give you something to work with next time around.

Cheers.........Howard

I agree that you would record the value if measuring but there is actually no requirement in 612.2.1 to record any value of resistance during a continuity test on initial verification.

If you have a continuity 'buzzer' operating at a voltage of between 4 and 24 V dc or ac with a short circuit current of not less than 200mA then you've complied with every part of 612.2.1 for the continuity of protective conductors test.
 
I've done live testing (including Zs) on every NICEIC and ECA technical assessment that I've ever done (a few) all without any comment from the assessor.

The NICEIC official line stems from the EAWR 1989 and the lack of distinguishing between 'working live' and testing.

IQ, Live testing is considered working live by the HSE in HSR25.
EAWR 1989, Regulation 14, is absolute (no deviation allowed, and work is defined as any work activity not just electrical), therefore ALL three of the following conditions, in ALL circumstances must be met before a person may work live.
"Regulation 14, Work on or near live conductors.
No person shall be engaged in any work activity on or near any live conductor (other than one suitably covered with insulating material so as to prevent danger) that danger may arise unless:
a) it is unreasonable in ALL the circumstances for it to be made dead; and
b) it is reasonable in ALL the circumstances for him to be at work on or near it while it is live; and
c) suitable precautions (including where necessary the provision of suitable protective equipment) are taken to prevent injury.

HSR25 Memorandum of guidance on the EARW 1989, Regulation 14 guidance paragraph 208, states "Live work includes live testing ... ".
 
Last edited by a moderator:
IQ, Live testing is considered working live by the HSE in HSR25.
EAWR 1989, Regulation 14, is absolute (no deviation allowed, and work is defined as any work activity not just electrical), therefore ALL three of the following conditions, in ALL circumstances must be met before a person may work live.
"Regulation 14, Work on or near live conductors.
No person shall be engaged in any work activity on or near any live conductor (other than one suitably covered with insulating material so as to prevent danger) that danger may arise unless:
a) it is unreasonable in ALL the circumstances for it to be made dead; and.....It could be argued that a Zs test is required and cant be completed dead
b) it is reasonable in ALL the circumstances for him to be at work on or near it while it is live; and..It is if he is competant to be in the proximity.
c) suitable precautions (including where necessary the provision of suitable protective equipment) are taken to prevent injury....Using an approved ELI tester in the correct manner is surely taking suitable precautions using approved safety equipment

HSR25 Memorandum of guidance on the EARW 1989, Regulation 14 guidance paragraph 208, states "Live work includes live testing ... ".

That would be my interpretation of the above guidance.....other interpretations might be devised. The problem is,with the present litigation culture,as soon as something goes wrong the sort of ambiguous guidance above will always be interpreted as live testing should not have been carried out, in order to dump on the individual concerned from a great height.
 
There's alot of sparks that test properly doing ALL tests correctly getting all value readings, yet there so many out there that I'm up against that do PIR's for £99, some of my competition must be bull s*****s, your day is easily took up doing PIRs correctly, or there just prepared to work for nothing.
 
"Regulation 14, Work on or near live conductors.
No person shall be engaged in any work activity on or near any live conductor (other than one suitably covered with insulating material so as to prevent danger) that danger may arise unless:

a) it is unreasonable in ALL the circumstances for it to be made dead; and

HSR25 Memorandum of guidance on the EARW 1989, Regulation 14 guidance paragraph 208, states "Live work includes live testing ... ".
Does that mean we HAVE to pull cut-out when working in CU - let alone replacing it.

Oh! Wash my mouth out with WD40.
 
Does that mean we HAVE to pull cut-out when working in CU - let alone replacing it.

Oh! Wash my mouth out with WD40.
Now that is a question, and the answer is probably why no one ever gets in trouble for doing such.
From a legal standpoint, can it be illegal to carry out an action that safeguards a person's safety?
 
We are trained electricians electricity is our life , i just want to grab hold of the spec wearing pen pushing person that says you cant do this live oh for gods sake , like a driving schoolyour driving lesson you cant start the car up or move it just in case you crash , there are more people injured in cars so when are they going to ban them , you always treat circuits as if they were live even when you know they are dead then there is not a problem , yes maybee for a trainee who's never carried out electrical work then fair enough thats why there is training , how many places have banned step ladders , they are very safe if used correctly if not you fall off , and working plat forms arnt the be all and end all i had 6 cable clips to put in i worked off a platform fell and ended up in casualty ,slipped off a step silly thing to do if i was using stemps it wouldnt have happend sorry for going off on one just get so dam frustrated !!!!
 
I must admit, it often makes me chuckle when sitting in on site inductions we are told to treat all cables as live, and not to touch them or we'll be chucked off site.
 
We are trained electricians electricity is our life , i just want to grab hold of the spec wearing pen pushing person that says you cant do this live oh for gods sake , like a driving schoolyour driving lesson you cant start the car up or move it just in case you crash , there are more people injured in cars so when are they going to ban them , you always treat circuits as if they were live even when you know they are dead then there is not a problem , yes maybee for a trainee who's never carried out electrical work then fair enough thats why there is training , how many places have banned step ladders , they are very safe if used correctly if not you fall off , and working plat forms arnt the be all and end all i had 6 cable clips to put in i worked off a platform fell and ended up in casualty ,slipped off a step silly thing to do if i was using stemps it wouldnt have happend sorry for going off on one just get so dam frustrated !!!!

agree 100%, nick. whilst safe working practice is essential, if the red tape and nonsense were to be cut and more common sense applied, the only down side would be more "suits" on the dole.
 
I must admit, it often makes me chuckle when sitting in on site inductions we are told to treat all cables as live, and not to touch them or we'll be chucked off site.

Sat through a site induction even though i had my CSCS card wouldnt let me on site otherwise ,went through the whole safety manual well it felt like it 11/2 hours of it , all i had to do was reset an MCB , funniest thing was it was in the office the site induction took place !!!

Tel now that would be a shame lol but what i will say i think it may well back fire because youngsters will not see the dangers , and will probably end up getting injured by the thing they are least lickly to get injured by , dont get me wrong im all for Health and safety it saves lives but feel its over the top
 
In short, to the first part, you can calculate Zs, how ever never can you calculate Ze or R1+R2.

reasoning behind this is Zs only tells us an earth fault path nothing more.

Ze tells us we have an acceptable earth (not a path through the bonding etc)
R1and R2 tells us we have a physical return path via CPC (Not through parallel paths etc)

Never calculate R1+R2 or Ze

the whole working live thing..

it is unreasonable in ALL the circumstances for it to be made dead; this bit here tells us we can work live when testing... as pointed out we have to carry out Ze and Zs testing along with RCD and Ipf. we cannot and never will be able to test the when dead, and therefore have to test live.
 
We don't have to test Ze or PFC as they can be determined by enquiry.
Zs can be calculated using the measured R1 + R2 value added to the enquired Ze value.
That just leaves the RCD test.
 
We don't have to test Ze or PFC as they can be determined by enquiry.
Zs can be calculated using the measured R1 + R2 value added to the enquired Ze value.
That just leaves the RCD test.

Yes, Spin's absolutely correct, the above are all accepted ways of deriving the figures to fill in the form, but not one of MY forms, my values are measured and confirmation of an adequate means of earthing etc. is obtained.

I guarantee that I can take a better guess at Ze and then PFC figures than any chap at the DNO can give me!
 
Agree with both the Spin and the IQ, though mostly an enquired Ze would only really be seeked at a designed stage, though in some cases I have known Ze obtained by enquiry on a large industrial complex where gaining access to take a measurement was virtually impossible during a PIR as it would mean closing down the entire complex. Not ideal but it is there for such occasions
 

Reply to Who does just a Zs when carrying out a periodic on a lighting circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top