hi guys,

Just wanted some help with some course work for college. Any help is greatly apprecitaed.

Why should a low value earth fault impedance should be achieved for all circuts?

thanks
 
OK< in simple terms. think ohm's law. I=V/R. V is fixed at 240v (single phase) . the value of R ten determines the fault current. the lower the vale, of R, the larger the fault current. if you look at the time/current curves in app.3 of BS7671, you will see that the higher the fault current, the quicker the fuse/MCB will trip, thus isolating the circuit. the quicker it does this, the better.
 
so its importnat to have the low value earth fault impendance so the current is flowing freely and will be higher. it will then trip the circut breakers quicker under fault conditions as its got less current to increase to that trip point!

am i getting it now?
 
think you are there. apart from the last bit .
 
Be careful of the terminology too. You need to refer to "Causing the operation of the protective device"
In an exam like 2391 terminology can get you a fail. Obviously if you're at a low level they may let you by because they know what you mean but it's good to get into the habit ofusing the corrct terms
 
If your earth loop is too low, then the overcurrent device will NOT be able to stop the fault the current, and in effect weld the MCB.

Very rare I might add, but might make you understand better.
 
If your earth loop is too low, then the overcurrent device will NOT be able to stop the fault the current, and in effect weld the MCB.

Very rare I might add, but might make you understand better.

Or as we usually put it 'a high PFC' ;)
 
Its like this. Ohms law.

230v with an earth loop impedance of 0.1 ohm. (Good)
230/0.1=2300A.

So 2300a of fault current will flow in the circuit.

Lets assume the circuit is protected by a BS60898 16a B type MCB

2300a in this particular circuit will disconnect almost instantly, and so comply with the 0.4 second disconnection time. The difficult to understand tables in the BGB will give you an exact time.

Now lets look at poor EFLI

230v/10ohm=23a.(Bad)

23a fault current in this circuit, again from the difficult to understand tables in the BGB, we can see that this circuit will disconnect in about 10,000 seconds, thats about 2.5 hours, so it does not meet the 0.4 second disconnection time. Bear in mind that current of about 80mA can kill you, then 23a for 2.5 hours wont be much of a laugh.

This is why we need a very low loop impedance and this is why the suppliers state TN 0.8ohm Ze, and TNCS 0.35ohm Ze as a maximum.

The figures i quote from the BGB may not be accurate, as i have done this off the top of my head, but you get the picture i hope.

Cheers..........Howard
 

Reply to why a low earth fault loop impedance in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
556
Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
742
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Hi all. I recently failed a section of my AM2E assessment. Passed 7/10 but failed on some silly things I'm confident of correcting second time...
Replies
1
Views
400
Hi guys was having a conversation as a apprentice I’m still not sure and was wondering why earth fault loop impedance is important if you’ve...
Replies
9
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock