Discuss Why did 60 Amp breaker pop in the UK Electrical Forum area at ElectriciansForums.net

Kenewber

DIY
Reaction score
7
New member and DIY. I have a 60 AMP breaker going to a sub panel for a workshop. Two months ago I bought an electric car and a 40 AMP charger that I wired a 50 AMP breaker to my sub panel.

I charge from midnight to 7 am and everything has been fine for 2 months. Last night the main 60 AMP breaker popped several times after resetting it but the 50 AMP which is directly wired to the charger did not.

My charger allows me to adjust the output and I lowered it from 40 to 30 amps and it popped again. I then lowered it to 20 AMPS and it did not pop again.

Can anyone give me a clue as to why the 60 AMP breaker popped. The only thing running on the sub panel was the charger.

Thanks very much for any help. Ken.
 
I would change the old 60A breaker for a new one, if the problem persists then you have a fault that needs investigating, do not keep resetting it.
if the problem goes away then it is reasonable to assume the breaker was faulty.
 
Yes, I have a worshop but all tools and lights were off. I even turned the new breakers off of everything except the charger and it still popped.
That brings it down to one (or worst case more) of:
  • The 60A breaker is faulty
  • The cable run has a fault
  • The charger has a fault
Altering the charge setting appears to stop it, so cable is less likely, and I suspect a replacement breaker is the cheapest test to rule that out before you consider the expensive case of a faulty charger.

Just to check this is over current only simple breaker, not a GFCI/RCBO unit?
 
That brings it down to one (or worst case more) of:
  • The 60A breaker is faulty
  • The cable run has a fault
  • The charger has a fault
Altering the charge setting appears to stop it, so cable is less likely, and I suspect a replacement breaker is the cheapest test to rule that out before you consider the expensive case of a faulty charger.

Just to check this is over current only simple breaker, not a GFCI/RCBO unit?
Thanks very much for your reply. I installed
a new breaker and it appears to have fixed the problem since I charged at 40 amps last night with no problem.
 

Reply to Why did 60 Amp breaker pop in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I will describe my problem in as much detail so you guys might be able to answer my question. I am never home, my Electric bill is $ 28 to $30 a...
Replies
23
Views
1K
Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Replies
6
Views
854
I’m planning a 240V welder circuit in a detached garage with a 100A sub panel. For the 160A or 180A output welders I’m looking at, the conductor...
Replies
5
Views
938
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
1
Views
688
Good afternoon - we're considering adding an additional breaker to our "main service panel" which is where the meter is located. That panel has 6...
Replies
1
Views
695

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock