Discuss Why did GFCI receptacle fail after one day? in the UK Electrical Forum area at ElectriciansForums.net

alekdavis

DIY
Reaction score
1
A 13-year-old GFCI kitchen receptacle went bad, so I replaced it with a new one I bought from Lowe's (Eaton model TWRSGF20). After one day, this one failed as well (the red dot is flashing with the yellow dot solid which, according to the manual, means it needs to be replaced). I cannot reset the receptacle. I also tried resetting the breaker, but it did not make a difference. Could it be just a defective receptacle or is there something going on in my electrical circuit? A while back I had to replace a breaker that was constantly tripping (on a different line), but in this case, the breaker did not even trip. If it's important, the circuit controlled by the GFCI receptacle is not loaded. I have a bunch of small appliances connected to it but I did not use any of them after I replaced the unit. Any ideas what could be going on here?
 

Attachments

  • PXL_20230610_073852587.jpg
    122.2 KB · Views: 3
Most likely it is a bad unit as often parts with manufacturing faults fail shortly after being put in to use. See:

I have not checked the LED fault info so if it really is saying faulty then faulty it is. However, you can get RCD (GFCI) tripping if there are faults in the supplying wiring, but that would hopefully cause a different diagnostic LED pattern.

Also have you had thunderstorms recently? Sometimes lightning surges can take out electronics stuff, even though they ought to be hardened to some degree. That is why new installs are normally fitted with a SPD (Surge Protection Device).
 
A 13-year-old GFCI kitchen receptacle went bad, so I replaced it with a new one I bought from Lowe's (Eaton model TWRSGF20). After one day, this one failed as well (the red dot is flashing with the yellow dot solid which, according to the manual, means it needs to be replaced). I cannot reset the receptacle. I also tried resetting the breaker, but it did not make a difference. Could it be just a defective receptacle or is there something going on in my electrical circuit? A while back I had to replace a breaker that was constantly tripping (on a different line), but in this case, the breaker did not even trip. If it's important, the circuit controlled by the GFCI receptacle is not loaded. I have a bunch of small appliances connected to it but I did not use any of them after I replaced the unit. Any ideas what could be going on here?
My friend it could be a defective GFCI receptacle, I’ve installed many that was bad straight out of the box. Replace it with a new one and see how it works out for you.
 
Most likely it is a bad unit as often parts with manufacturing faults fail shortly after being put in to use. See:

I have not checked the LED fault info so if it really is saying faulty then faulty it is. However, you can get RCD (GFCI) tripping if there are faults in the supplying wiring, but that would hopefully cause a different diagnostic LED pattern.

Also have you had thunderstorms recently? Sometimes lightning surges can take out electronics stuff, even though they ought to be hardened to some degree. That is why new installs are normally fitted with a SPD (Surge Protection Device).
Thank you. There were no thunderstorms, so it shouldn't be the reason. I'll try replacing it with another unit.
 
My friend it could be a defective GFCI receptacle, I’ve installed many that was bad straight out of the box. Replace it with a new one and see how it works out for you.
Thank you. I will try another one and post if it continues to be a problem. Hope you're right and it's a defective device.
 

Reply to Why did GFCI receptacle fail after one day? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a small power washer with a two-wire cord and GFCI plug. My outdoor and garage receptacles are on a "house GFCI" circuit, wired in series...
Replies
2
Views
2K
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
561
Upfront disclosure, I am a DIY homeowner with basic knowledge of electrical safety. Here is my issue: Type GFCI Outlet- Eaton TR Installed mid to...
Replies
2
Views
1K
I have installed a GFCI breaker the main panel which feeds a circuit that serves two bedrooms. This was done so I could replace all the old non...
Replies
5
Views
1K
Background Two weeks ago, lightning struck a tree in our yard. Many circuits tripped and several electronic devices failed. There was a strong...
Replies
2
Views
870

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock