Rob Plant
DIY
- Reaction score
- 0
With apologies in advance for the newbie question...
I'm using a multimeter to figure out the source of my battery drain, so attempting to measure the leakage current between my battery terminal and its lead. When taking the readings shown below, they are quite steady, but as you can see, on the 10A setting I get a measurement of (-)69 mA, while on the mA setting I get 1.5 mA. Is this just because of the lower resolution (and higher error) in the 10A mode? I ask because online how-to information for doing this say to do the check in the 10A mode, and to be concerned if the current is more than about 50 mA. Based on the mA settign reading, I see no problem, but is there reason for concern based on the 10A reading?
I'd appreciate any pointers - thanks!
Rob
I'm using a multimeter to figure out the source of my battery drain, so attempting to measure the leakage current between my battery terminal and its lead. When taking the readings shown below, they are quite steady, but as you can see, on the 10A setting I get a measurement of (-)69 mA, while on the mA setting I get 1.5 mA. Is this just because of the lower resolution (and higher error) in the 10A mode? I ask because online how-to information for doing this say to do the check in the 10A mode, and to be concerned if the current is more than about 50 mA. Based on the mA settign reading, I see no problem, but is there reason for concern based on the 10A reading?
I'd appreciate any pointers - thanks!
Rob