What is very different though is the use of a 63A B-curve MCB as input isolator.

Certainly I think isolation should always be all-pole (though for TPN that is not so common and ideally then you want a mate first / break last on N) and I was surprised that ROI did not do so in the past.

The use of the MCB to me is kind of mixed, I can see it is a good idea to limit each CU's total current without pushing the DNO fuse in to that job (I presume ROI still has the equivalent of a fuse as ultimate limiter?) but it also seems a bad idea on selectivity as many high current faults will take out both the faulty circuit and the whole damned supply!

63A B-curve instant trip is 189-315A, though looking at the Hager tables it would be selective with a 20A B-curve for socket radial to around 700A. That is still less than often seen for PSSC on sockets here (my experience mostly the RFC, maybe easier at ends of 20A radial though?).

What we have is an MCB at the supply cabinet

Double pole main isolation at the main board
then

Its mostly similar to UK on the boards , heading toward all RCBOs
 
remindsme of the air fungus pilot sends out a mayday. controller asks him his height and location.....

" Oi'm 5 ft 10in. and sitting at the front. of this machine"
 

Reply to Why do we do it the way we do in the UK? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've been installing Type 2 SPDs in consumer units for several years now, and they always come as a pair, connected across L & E, and across N &...
Replies
2
Views
560
I got one of these ready built consumer units for my father in laws EV install. Got the cables run in, mounted the charge point etc…. Then took...
Replies
24
Views
3K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
296
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
690

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock