Discuss Why doesn't my Security Light work? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
8
I have a Security Light on my patio and until recently it worked fine.
It stopped working and I couldn't decide if it was the LED Floodlight or the separate PIR that had stopped working so I replaced both.
I checked them out first, connected them up and they work fine on my workbench, but then I install them outside and they won't work.
I've attached a wiring diagram showing how they are connected.
It all seems straight forward and the wiring is exactly the same as the old set-up so I'm at a loss as to why they don't operate.
Any useful ideas?
 

Attachments

  • Security Light 01.jpg
    39.4 KB · Views: 5
If they work on a bench, from a different supply, then it's neither the LED light or PIR, it's a fault on the supply from within the house.
Have you checked you have both Live and Neutral (and earth) at the PiR position on the property and that the switched Live and the Neutral are continuous to the LED light,?

Have you tested the old light and PIR on the bench?
 
If they work on a bench, from a different supply, then it's neither the LED light or PIR, it's a fault on the supply from within the house.
Have you checked you have both Live and Neutral (and earth) at the PiR position on the property and that the switched Live and the Neutral are continuous to the LED light,?

Have you tested the old light and PIR on the bench?
To answer your two questions:
1. Yes, I've tested the mains supply to the outside world and it appears to be OK - my AVO tells me it is anyway.
I did wonder if it's my connections at the choccy block in the junction box and/or the PIR; i.e. I'd screwed onto insulation instead of cable, so I've undone everything and checked the screws are clamping onto cable and not insulation. I've even tinned the cable ends so they're solid instead of just twisting the cable cores.
2. When I connected up the old system on the workbench the PIR worked OK with the new flood, but the old flood didn't work - even when connected directly to a supply rather than through the PIR so I guess it was the flood at fault, but I happened to have a brand new, still in the box, PIR available, that's why I changed both.
 

Reply to Why doesn't my Security Light work? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

can anyone please advise on where the wires go? My electrician installed a new cable ready for when I bought a security light. The cable as shown...
Replies
3
Views
540
Hi all, H.N.Y. The passive, affixed to a recently bought LED security light is rubbish, sometimes it works, mostly it doesn't, no matter how...
Replies
2
Views
461
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
532
I've just changed the bulb in an outdoor PIR security floodlight (to LED). But the light stays on by default, and turns off when I go outside. I...
Replies
1
Views
934
Hi. I'm an I.T.. engineer with some outdated electrical experience. I qualified C&G 2330 17th edition about 15 years ago, but my only experience...
Replies
4
Views
790

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock