Discuss Why dont we use 1/2 amp fuses anymore explained in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
If the appliance has 0.5 sq mm cable, the UK plug should (maybe "must" because of the wording in the Plugs and Sockets Regulations) be fitted with a 3A fuse, or 5A if high inrush.


If the appliance has 0.75 sq mm cable or above, the UK plug should be fitted with a 13 A fuse.


Before you get to selecting fuse size, you have already selected the cable based on the following (in Table 2 of BS1363-1 as mandated by the Plugs and Sockets Regulations):


Appliance Rating Cable Size
<=3A 0.5 sq mm or greater
<=6A 0.75 sq mm or greater
<=10A 1.0 sq mm or greater (0.75 is allowed if <2m cord)
<=13A 1.25 sq mm or greater


(noting the max size that will fit in a UK plug is 1.5 sq mm).


These rating figures are determined by the temperature the cable may reach in operation.


The fuse size is determined by using a "non-adiabatic" method, looking at whether the cable will overheat in a direct short-circuit.


The only limits on flex length (apart from 0.75 sq mm with a 10 A appliance) are relating to volt-drop (or Class I touch voltage), and not short-circuits.




So, how does this relate to your tin opener?


Assume current < 3A, manufacturer must choose flex not less than 0.5 sq mm (from Table 2 of BS1363-1). So he chooses 0.75 sq mm. Then needs to size fuse, and again refers to Table 2 of BS1363-1 which says that 0.75 needs 13 A fuse.


Manufacturer then ensures (with the aid of the appliance safety standard - in this case the appropriate parts of BS EN60335, I'd guess) that the tin opener will not cause fire or shock or burns in a fault with the selected fuse let-through, and presto - design complete.
 
Don't ever copy/paste complete replies written by other people from other forums.

It reeks of either you're misleading people into thinking the text is your work which is theft or fraud or you're starting a discussion using someone else's statements and opinions and they're not aware and aren't able to elaborate, expand, explain or defend their remarks that have been taken out of context.

The original thread is here IET Forums - What does a fuse protect!!!

This thread is closed and due for deletion in the near future.
 

Reply to Why dont we use 1/2 amp fuses anymore explained in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Greetings everyone. My first post here, having read a similar thread, I understand that following the manufacturers guidance is all important...
Replies
10
Views
8K
S
Hi there I'm working in a pizza take away doing the installation for it . Just recieved The kitchen appliances rundown and now planning my final...
Replies
8
Views
6K
Specialist
S
S
Hello all I was wondering if anyone could help me understand why our toaster came with a 0.75 sq mm flexible cable with 13A BS1362 fuse on the...
Replies
7
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock