Interesting, A while ago I had conduit CPC fail on 2 circuits with 50-150ohm Zs, I pulled through a new CPC for one of them, and for the cooker ran a new bit of T&E as was close to CU.

Although I believe this is the best way to fix it as now has a nice low Zs and meets disconnection time for the MCBs, But in theory if the circuits were on an RCD or upgraded to be on an RCD then could have been left like this as the 150ohms is enough to meet disconnection due to the RCD.

If it was to later have an EICR though I cant imagine many people passing it without a code as the r1+r2 would be high
This is where experience and common sense kicks in (hopefully)....if such a reading was obtained on a TN system clearly alarm bell should ring despite the presence of an RCD, and if a TT was in place you would hope an experienced person would verify that the high reading was due to the Ra and not a wiring issue.
Experience electricians recognise when a problem exists regardless of the regulations.
 

Reply to Why is a too high zs reading on a circuit okay if it’s protected by an Rcd? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
998
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Does a RCBO protecting a single circuit mean it can have a maximum Zs of 1667 Ohms since it's being used as fault protection?
Replies
3
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock