Discuss Why live to ground voltage is only 0V (in a 220V AC power outlet, there is also electric shock)? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hello, my name is Kelvin. I'm a trainee hydraulic engineer in Indonesia. I apologize if this question has been answered before / if this question is too basic. So we have a problem with electric shock coming from an electric panel. This panel runs on 220V AC supply & is used to run an inverter (single phase input & three phase output) to run a three phase electric motor. We checked the supply voltage from live to neutral, live to ground & neutral to ground. The result is shown below:
Live to neutral (panel).jpeg
Live to ground (panel).jpeg
Neutral to ground (panel).jpeg

then we checked the electric outlet where the power for the panel is coming from. We measured the voltage again, but the result for 'live to ground' voltage is different
Live to ground (power source).jpeg
Live to neutral (power source).jpeg
Neutral to ground (power source).jpeg

As you can see, the voltage from live to ground at the power outlet is only 0V, but the one in the electric panel is 133V
Are there any possible reasons for this to be happening? Might this the reason an electric shock is happening on the panel?
Here is the electrical diagram for the panel.
Electrical Diagram - OFT120 SIS.png


Thank you in advance for your help, any sorts of comments are appreciated :)
 
looks like a broken ground connection to me.
measure from ground at outlet to ground at machine and I expect you will find 100v or more.
 

Reply to Why live to ground voltage is only 0V (in a 220V AC power outlet, there is also electric shock)? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I experienced an electrical shock while replacing an A/C Fan Coil's 120vac, single phase motor that was above the ceiling grid in an office, while...
Replies
46
Views
4K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
I have a Single Phase Power box for a townhouse. When I read voltage across the Hot legs (A) and (B) to ground I get 123 volts with the main...
Replies
1
Views
973
Good afternoon all, today I experienced a near death electric shock. This happened on a single phase domestic property! I was carrying out a few...
Replies
15
Views
3K
Hi, Apologies if this is in the wrong forum. I do have another account on here which I would imagine is not allowed by admins - this account will...
Replies
31
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock