Discuss Will a B type 32 trip before a C type 16? in the UK Electrical Forum area at ElectriciansForums.net

GBDamo

-
Esteemed
Arms
Reaction score
3,010
Morening all,

I have a dilema that you may be able to help with.

Manufacturers instructions ask for the unit to be fed from a C Type 16Amp MCB. At the moment this is all the technical information I have.

In one in twenty cases they experience nuisance tripping and have now recommended fitting a C type 16 Amp MCB.

Units have previously been fed from 13 Amp FCUs and it would be my intention to feed a locally mounted and enclosed C16 from that FCU.

Ideally I'd like to change the MCB at source but in all likelihood Zs's wont allow that.

Does the brain trust know of a more elegant way to solve this?

Thanks in advance, will look back in later today as on the road at the moment.
 
Hi - Can you clarify the roles of 32A B, 16A C and the 13A fuse please ? Also, what is the load and what's the existing circuit cable and Zs?
 
You'll need to compare the curves and understand the type of overload that is causing the nuisance trip. For example, between 18 & 36A (1.13xIn for each MCB) the 16A should trip but the 32A should not, regardless of the type, as only the thermal tripping mechanism will operate. But at 128A (8xIn for B16 and 4xIn for the C32) either or both magnetic trips may act; the tripping time could be anywhere between a few milliseconds and a few seconds and there's no way to predict which will go first.
 
For example, between 18 & 36A (1.13xIn for each MCB) the 16A should trip but the 32A should not
Below 1.13 In the device must not operate, but at 1.45 In it must operate within the conventional time (1 hour). So between 1.13 and 1.45 In is open.
 
Hi - Can you clarify the roles of 32A B, 16A C and the 13A fuse please ? Also, what is the load and what's the existing circuit cable and Zs?

Thanks for the reply’s and sorry for the delay in responding.

The “unit” is a dental chair but have not yet seen what or how the load is used or why the manufacturer has now requested a C16 MCB.

Just a panicked call asking whether we can achieve this by putting an MCB in line between the chair and FCU.

I appreciate I need more information but was half hoping it might be a definitive yes or no.

I reserve the right to resurrect this post when I have a clue what I’m talking about.

Cheers though.
 
Thanks for the reply’s and sorry for the delay in responding.

The “unit” is a dental chair but have not yet seen what or how the load is used or why the manufacturer has now requested a C16 MCB.

Just a panicked call asking whether we can achieve this by putting an MCB in line between the chair and FCU.

I appreciate I need more information but was half hoping it might be a definitive yes or no.

I reserve the right to resurrect this post when I have a clue what I’m talking about.

Cheers though.
I would think the munufacturers requested a C OCPD type because the " unit has inherent inrush problems" I'm going to stick my kneck out here and say, perhaps with your background you should stick to what you know Domestic Installations.
 
What’s the point in installing a 16A mcb downstream of a 13A fuse?

This sounds suspiciously like the dentists chair is being fed from a ring final circuit.
They pretty much all are.
I would think the munufacturers requested a C OCPD type because the " unit has inherent inrush problems" I'm going to stick my kneck out here and say, perhaps with your background you should stick to what you know Domestic Installations.
Domestic installation is one many things I know. I also know that of which I know not enough. Standing still in life bores me I like to learn new things.
 
Is this one of those chairs which have the compressor,vacuum and lighting all contained within?

It sounds like too heavy a draw,for just positional motors.
 
According to 41.3 in the regs, the Zs for the 16amp, type C is 1.37 ohms. 80% of tabulated is 1.1 ohms (rounded). With at least three connections (DB, FCU & local outlet) is 1.1 viable or is the solution a dedicated radial from the DB with the 16 amp type C? Just interested.
 
I do some work for a dentist that has her own surgery with five chairs in total. As far as I know all chairs are fed from FCUs or plugs. They have three DBs and I can't recall seeing any C curve breakers in any of them. Probably a different brand of chair. The surgery I do work for has a larger central compressor though that feeds all the chairs.
 

Reply to Will a B type 32 trip before a C type 16? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a small Consumer Unit fed from a 6 amp type B mcb to a 6 amp type B,it only feeds 1 light in a bin store . clearly we have no selectivity...
Replies
7
Views
585
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
900
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
886
Hello all.. I'm quoting for some work and would like change the type AC RCBO to a type A. Consumer unit is a castlec which I have not come...
Replies
5
Views
902
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock