Discuss Wiring a 1KW pool heat pump in the DIY Electrical Advice area at ElectriciansForums.net

TheGC2020

DIY
Reaction score
4
Hello. I was hoping someone could please help me with some queries?

I’ve just taken delivery of a single phase pool heat pump rated 1kw, with running amps of 4.5. Retailer has advised that it should be wired into a separate type C MCB with a min 10A fuse. I was hoping I could just put a standard 13A plug on it (perhaps with a 10A fuse) and plug it into an IP66 socket (either an RCD socket or with the socket on an RCD protected circuit) on a 2.5mm arctic blue type flex. Existing circuits are B curve type and rated 32A. Am I being naive, what am I missing?

The heat pump is to heat a temporary/semi permanent above ground pool and will also have a feed for a pump which should require no more than 500W. Not sure if the retailer is just taking a belt and braces approach as many of their other heat pumps are more powerful.

Your thoughts please? Thank you
 
TL;DR
1KW heat pump - does it have to have a separate supply as recommended or can it go on a 13A plug? B Curve type MCB okay or does it need to be a C curve?
Sir/Madam, this is a job for a qualified electrician who understands the risk factors, the UK regulations and how to design and install something safe and durable. He/she will (if not don't pay) inspect and test afterwards and provide you with a valuable certificate which is a very handy thing to keep safe somewhere, just in case.
 
Last edited:
Sir, this is a job for a qualified electrician who understands the risk factors, the UK regulations and how to design and install something safe and durable. He/she will (if not don't pay) inspect and test afterwards and provide you with a valuable certificate which is a very handy thing to keep safe somewhere, just in case.
Many thanks for the advice - that’s where I was coming to in my mind too. I know that there are special regs for pools and extra risks. Purely to satisfy my curiosity - do you know why a 1kw electrical device can’t go on a plug?
 
The manufacturer is suggesting the protective device at the consumer unit but there is no reason why it cannot be connected through a suitable 13A socket from a dedicated circuit or otherwise.
 
The manufacturer is suggesting the protective device at the consumer unit but there is no reason why it cannot be connected through a suitable 13A socket from a dedicated circuit or otherwise.

Many thanks - good to know my basic understanding was correct re the plug. Does ‘or otherwise’ mean there might be another option than running a new dedicated circuit from the CU as that’ll be a pita?
 
A heat pump has a compressor with a high starting current, typically 5x the running current if it is not inverter driven. They may have experienced problems with 13A plug fuses blowing, hence the suggestion to use a C-type MCB which is less likely to trip on the starting current. Since the higher instantaneous trip level requires a lower loop impedance on the circuit to maintain safety, they probably recommend a 10A MCB as the lowest they have found compatible with the compressor, to avoid onerous cable size requirements.

Note also that a device with high earth leakage current (>3.5mA) should not be connected via a 13A plug and socket; a more robust connector or hard-wiring is required to absolutely minimise the risk of the earth becoming disconnected. It is unlikely that this unit has such a high leakage current but that is another reason a 13A plug might be unsuitable for a specific application <13A.
 
A heat pump has a compressor with a high starting current, typically 5x the running current if it is not inverter driven. They may have experienced problems with 13A plug fuses blowing, hence the suggestion to use a C-type MCB which is less likely to trip on the starting current. Since the higher instantaneous trip level requires a lower loop impedance on the circuit to maintain safety, they probably recommend a 10A MCB as the lowest they have found compatible with the compressor, to avoid onerous cable size requirements.

Note also that a device with high earth leakage current (>3.5mA) should not be connected via a 13A plug and socket; a more robust connector or hard-wiring is required to absolutely minimise the risk of the earth becoming disconnected. It is unlikely that this unit has such a high leakage current but that is another reason a 13A plug might be unsuitable for a specific application <13A.

Ahhh making a lot more sense and good
to understand the reasoning - many thanks for taking the time for the informative response
 

Reply to Wiring a 1KW pool heat pump in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hey everyone, hope you all had a good xmas. Got called around to change over an old style pin type thermostat to a hive one for a family member...
Replies
1
Views
565
Hi Guys Just seeing if anyone can help please. Does this pump come with plug in type/ pre flexed feed (hopefully that makes sense!) as cant see...
Replies
4
Views
1K
Hi, I hope that someone here might be able to put my mind at rest. I have an engineering mind and a reasonable understanding of electical work...
Replies
13
Views
2K
I incorrectly posted this on the "electrician's forum" and got a bit of a cold shoulder. Looking for some tips on supplying my pool equipment...
Replies
4
Views
898

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock