Hi Guys,

My knowledge limited to just connecting a led light to a driver, but not with a dimmer, can anyone advise how to wiring these 3 items all together please?

Thanks
Leo

image1.jpeg
 
Pete,

Firstly, the dimmer goes in the mains (240V) side of the circuit.
If you read the back of the dimmer you'll see that it says 230V on it...
So it goes in the lead from the plug to the power supply, or whatever that box is......

Secondly, again, if you read the back of the dimmer, you'll see it says 40-600W (watts). Your LED wil be way less than 40watts so that dimmer is no use to you. You need a LED-compatible dimmer that is designed for low current dimming. The Varilight V-Pro are decent ones for this purpose.

Thirdly, the driver/power supply needs to be dimmerable. Is it??
Same for the LED itself.
 

Reply to Wiring a dimmer and a led light sample in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi :) I'm currently renovating my outbuilding. My electrician has fitted 10 conduit LEDs (that support both leading and trailing edge) and x4...
Replies
0
Views
209
I have a led panel that i want to dim. It is dimmable but without a dimmable driver. I have a dimmer module and a dimmer switch as shown in the...
Replies
0
Views
559
Hi all I've been changing the halogen downlighters in my house to LED's. I have three rooms that use dimmers, two of them have two switches each...
Replies
0
Views
381
Hi, Can anyone please advise on what LED recessed lights to buy and how to wire for media wall đź‘Ť
Replies
0
Views
320
I have 2 lights connected to 1 switch. I installed a led light fixture on one light, it had one red wire and one black wires. It was easy to match...
Replies
0
Views
306

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock