plasteredric

Hi Guys,

I've done a quick drawing of how I think I should be wiring in the thermostat. Can anyone take a look over it to see if i've got it right.

Cheers
IMG-20140110-02146.jpg
 
Looks about right to me, although when I tilt my iPad it's rotating the drawing so I'm looking at it side on. Only thing that might change is your L1 L2 LX connections, depends on the contacts with the thermostat, it'll either work properly, not work atol or work continually bypassing the thermostat
 
sorry i'm not technical when it comes to electrics, what's the common?

this is the wiring diagram from the stat
IMG-20140110-02147.jpg


From what you've said im guessing it should be live to LX, then neutral from L1 back to boiler?
 
It's not essential to get colour correct on the switching side, but for simple ness, brown LX and blue L1 as u said.

Colour/polarity must be correct on the mains side tho ..... Which as you've put brown-live ,blue-neutra

no earth as item is double insulated.....
 
It's not essential to get colour correct on the switching side, but for simple ness, brown LX and blue L1 as u said.

Colour/polarity must be correct on the mains side tho ..... Which as you've put brown-live ,blue-neutra

no earth as item is double insulated.....

Careful there ........ The thermostat may well be double insulated, but the boiler isn't.

Don't confuse the op into thinking there is no need for an earth on the whole installation!

You know what you mean and so do I and most of the other lads will too, but we can't take it for granted that the op does. ;)
 
I like to use 5 core, but I'm caught short of 5 core, then 2 lengths of 3 core neatly tie wrapped together with appropriately sized cable ties is ok.

Wouldn't a 5 core be excessive in this case? im assuming you mean 5 cores + earth. or does it not matter about the spare wire?

Also, should the boiler be on it's own circuit from the RCD unit?
 
Wouldn't a 5 core be excessive in this case? im assuming you mean 5 cores + earth. or does it not matter about the spare wire?

Also, should the boiler be on it's own circuit from the RCD unit?

It's horses for courses.

The last job I did was a wireless stat. The transmitter was stuck on the wall in a living room and the receiver I mounted in a twin back box ( NOT to be confused with a double back box ) along with the fcu so the wiring from the fcu went to the receiver to power it and then on to the boiler via 3 cores of the 5 core (LNE) leaving 2 remaining cores from boiler to receiver and return from receiver to boiler to control it.

It isn't the "only" way to do it, but in the scenario I had it was the tidiest.

My old gaffer used to say "there's more ways to choke a pig than by stuffing it with butter".


Edit ..... the boiler circuit should be rcd protected and wherever possible I used to run it on its own radial from the cu, but it can be run as a spur.
 
Last edited by a moderator:
Careful there ........ The thermostat may well be double insulated, but the boiler isn't.

Don't confuse the op into thinking there is no need for an earth on the whole installation!

You know what you mean and so do I and most of the other lads will too, but we can't take it for granted that the op does. ;)

sorry mate, good point, :oops: Lol
 

Reply to Wiring a thermostat to Baxi Combi boiler - is this the right way? in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hi folks, I'd like to get my Nest thermostat up and running with the gas combi boiler (Worcester Greenstar HIghflow 440 Standalone). FYI - I...
Replies
9
Views
1K
Hi I'm trying to figure out how to swap my standard myson thermostats for WiFi enabled ones - going to start with the simple one first - the one...
Replies
4
Views
927
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
986
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
448
Hey everyone, hope you all had a good xmas. Got called around to change over an old style pin type thermostat to a hive one for a family member...
Replies
1
Views
582

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock