Discuss Wiring heater that came with 3 phase plug to single phase in the DIY Electrical Advice area at ElectriciansForums.net

You're in the twilight zone with this kinda thing. Can you still get a refund or exchange for a more suitable product?

The answer is it might be possible to rewire it internally to run from a single phase domestic socket but it also might not be possible. The elements will work with the lower voltage but their heat output will be lower. It all swings around the fan, if it's a 400v 3-phase fan then it won't work on 230v single phase.

Does it mention any single phase conversion in the user manual? If you're really lucky they might have some links you can change around to make the 3-phase to single phase change. If the elements are rated 3kW on single phase that's pretty damn close to the maximum load allowed on a domestic plug and socket, in fact if you take the new nominal harmonized voltages it's actually slightly over 13Amps.
 
You're in the twilight zone with this kinda thing. Can you still get a refund or exchange for a more suitable product?

The answer is it might be possible to rewire it internally to run from a single phase domestic socket but it also might not be possible. The elements will work with the lower voltage but their heat output will be lower. It all swings around the fan, if it's a 400v 3-phase fan then it won't work on 230v single phase.

Does it mention any single phase conversion in the user manual? If you're really lucky they might have some links you can change around to make the 3-phase to single phase change. If the elements are rated 3kW on single phase that's pretty damn close to the maximum load allowed on a domestic plug and socket, in fact if you take the new nominal harmonized voltages it's actually slightly over 13Amps.

I can confirm it is a single phase motor.

If you would like I can supply a picture of the internal wiring?
 
I think you should address your questions and concerns to the company you bought it off, or the manufacturer!
 

Reply to Wiring heater that came with 3 phase plug to single phase in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
598
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
656
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
864
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock