My understanding is that all wiring in escape routes requires fixing with metal fasteners/clips (safe D clips) every 300mm on the horizontal and 400mm on the vertical. I am currently upgrading 4 blocks of flats for a housing association.

Hope this helps
 
In my view wiring would need to comply with 422.2.1 and 521.11.201, plasterboard will give up to a maximum of 30 minutes protection depending on specification and to what and how it is fixed. According to regs wiring systems need to be fixed with suitable fixings to non combustible fabric of building. The regs specifically state so not to hinder evacuation and firefighting activities. In my view this may well reasonably take place after the expected fire resistance of plasterboard.
 
I just done a load of flats in a old mill complex, the escape routes are all on cable tray mounted on the steelwork with all cables sat on top so will not fall in a fire unless it was with the building falling down itself.
 
I just done a load of flats in a old mill complex, the escape routes are all on cable tray mounted on the steelwork with all cables sat on top so will not fall in a fire unless it was with the building falling down itself.

Did you use any steel ties on the tray?

The generally accepted standard around commercial new builds these days appears to be steel ties every metre regardless of the fact the cables can't get off the tray.
 
Did you use any steel ties on the tray?

The generally accepted standard around commercial new builds these days appears to be steel ties every metre regardless of the fact the cables can't get off the tray.

Not in this case and BC are happy as the tray runs through support bars every 1500mm so even taking the tray out of the loop say it was damaged by falling material the cables still cannot drop down without been physically severed every few meters. I used metal ties on the F/A cables on a seperate traywork as this isn't run within the same set-up, all fixed to brick with mini anchor bolts (no plastic plugs etc).
 
The problem I may face is that we are going to convert an old bank into a coffee shop & the ceilings may b retained. We are being asked to use existing circuits where possible but until I do my site survey today I'm still a bit in the dark.

Putting cable trays or trunking above ceilings before they are erected is fine, it becomes a problem when the main contractor states that the existing ceilings are to remain.



In my view wiring would need to comply with 422.2.1 and 521.11.201, plasterboard will give up to a maximum of 30 minutes protection depending on specification and to what and how it is fixed. According to regs wiring systems need to be fixed with suitable fixings to non combustible fabric of building. The regs specifically state so not to hinder evacuation and firefighting activities. In my view this may well reasonably take place after the expected fire resistance of plasterboard.
 

Reply to Wiring in escape routes in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, I have two questions regarding wiring and containment on commercial property stairwells in Ireland. We are currently wiring a 3 story...
Replies
10
Views
804
Gents, What is your view from this this clause from BS5266? If you have a lobby with that is part of an escape route that has one fitting, I...
Replies
5
Views
794
Hi, could anyone advise, this is the fuse box for the private rental flat above ours, its at the bottom of there stairs which is there only escape...
Replies
3
Views
710
Hi. Looked at a job this morning for remedial work on an EICR. The inspection has noted the plastic consumer unit within the hallway cupboard and...
Replies
7
Views
2K
I'm in the military with 2 years left of service and want to become an electrician when I leave. What's the ideal route I can take to become...
Replies
0
Views
292

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock