Discuss Words of wisdom please re an installation condition report in the UK Electrical Forum area at ElectriciansForums.net

Many thanks for all your replies, I've uploaded a copy of the report as requested by pc1966. I really appreciate all the answers, thank you for all your input
Here's a picture of the current board - thanks again for all your input
 

Attachments

  • Consumer Board.png
    266.3 KB · Views: 40
I was typing a similar post to @pc1966
My opinion:
'the absence of supplementary bonding in the bath or shower' etc.
Becomes non-issue most of the time once a new consumer unit fitted and all circuits in room have RCD protection.
'the absence of earthing at socket outlet',
Can be anything from a wire fallen out to a bigger problem. Needs investigation to determine. Not normally too bad.
'a ring final circuit having a discontinuous conductor'
Needs investigation, if can't be easily resolved there are normally easy workarounds (split into two radials)
'absence of a circuit protective conductor other than a lighting circuit, supplying class 1 equipment.
This gives an idea of age of wiring - up to 1965 ish. If not lighting this needs looking at with urgency. It might be linked to the socket without earthing above.
'unsatisfactory electrical connections, such as type, number and size of conductors unsuitable for the means of connection'
'adequacy of cables for current-carrying capacity with regard to the type and nature of the installation.'
My reckless guess is these relates to size of main tails or earth. More info needed to determine. Quite often size of earthing and bonding on older installations are smaller than would be installed new. If it is that a board change would review these as part of the job.

In all circumstances I would plan on around £500-600 for a new consumer unit with RCD protection. That buys a lot of peace of mind while issues are investigated and plans made.
The last three issues are the main ones that concern me, the others can likely be sorted out or worked around.
Many thanks Tim that's really appreciated
 
I've looked through the report. The last page is a helpful summary. If it's still accurate I'd say you need as a minimum:
Supply earthing checking (though codings don't completely make sense for earthing type stated)
Gas bonding adding (this shouldn't usually be too hard)
Upstairs light and downstairs socket discontinuous earth conductors need checking and sorting
The lights mentioned need looking at regarding necessity of fire rating
New consumer unit
(The single socket under the consumer unit will be an easy fix)

It should be noted that the upstairs lights and the downstairs sockets were not able to have any meaningful test performed on them due to the broken earths, so the insulation resistance tests which confirm the wiring is in good condition couldn't be carried out.

There is possible evidence further alterations have taken place since that report, such as spare circuit 1 now saying "Shower" on the consumer unit.

Personally, I would not exchange until:
1) You have an answer about whether any remedial works were carried out, with receipts if they claim any have been performed.
2) If no remedials, you arrange for a new EICR by an electrician of your choosing and an appropriate discount is mutually negotiated to cover remedial work. OR
3) You ask for a discount to cover part/full cost of a new consumer unit being installed. (easier)

All the best with this.
 
I've looked through the report. The last page is a helpful summary. If it's still accurate I'd say you need as a minimum:
Supply earthing checking (though codings don't completely make sense for earthing type stated)
Gas bonding adding (this shouldn't usually be too hard)
Upstairs light and downstairs socket discontinuous earth conductors need checking and sorting
The lights mentioned need looking at regarding necessity of fire rating
New consumer unit
(The single socket under the consumer unit will be an easy fix)

It should be noted that the upstairs lights and the downstairs sockets were not able to have any meaningful test performed on them due to the broken earths, so the insulation resistance tests which confirm the wiring is in good condition couldn't be carried out.

There is possible evidence further alterations have taken place since that report, such as spare circuit 1 now saying "Shower" on the consumer unit.

Personally, I would not exchange until:
1) You have an answer about whether any remedial works were carried out, with receipts if they claim any have been performed.
2) If no remedials, you arrange for a new EICR by an electrician of your choosing and an appropriate discount is mutually negotiated to cover remedial work. OR
3) You ask for a discount to cover part/full cost of a new consumer unit being installed. (easier)

All the best with this.
Many thanks, Tim, that's really appreciated, it's much clearer now. Thanks to everyone for their input
 
I'd opt for either proof of works being completed or getting another report carried out.

There are couple of "faults found" (fuse size too low for type of circuit) which to me aren't faults.

Ring main end to ends look quite low (I don't to a lot of domestic so these could look correct to someone else).

The sparky has also listed the kA rating of the MCBs as being 0.2 so maybes a typo here and there?
 
I'd opt for either proof of works being completed or getting another report carried out.

There are couple of "faults found" (fuse size too low for type of circuit) which to me aren't faults.

Ring main end to ends look quite low (I don't to a lot of domestic so these could look correct to someone else).

The sparky has also listed the kA rating of the MCBs as being 0.2 so maybes a typo here and there?
Thanks ToonSparky, I appreciate the comments. We hope to hear today what work has been done, then armed with everyone's input we can decide how to proceed. My daughter loves the house, so doesn't want to lose it but they did pay over the asking price, so there should be some leeway.
 

Reply to Words of wisdom please re an installation condition report in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
The seller is saying they will not upgrade the electric and it is normal to have 100 amps. However the inspector is stating it may trip often and...
Replies
4
Views
863

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock