Discuss Work out breaker size? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi, I'm a first year apprentice... just trying to get an edge on theory.

Calculating breaker size:

W ÷ V = A

So say appliance needs 4000 watts

4000w ÷ 230v = 17.39amps

Then, from research I seen a rule that the breaker shouldn't be running above 80% of it specific ampacity, so you multiply your amps by 1.25.

17.39amps x 1.25 = 21.73amps

So that would mean a 25amp breaker would be needed... like I said I'm only learning, if this is wrong, advice?

Many thanks
 
Last edited by a moderator:
What you’re referring to is known as “Design Current” or “Ib”

This is the amount of current that an item of electrical equipment will use under normal use. It’s the maximum current that will flow to operate the equipment.

Using the Power Triangle. P I and V (Look it up for a picture) You can work out the design current.

Here is an example for a purely resistive load such as an electric heater. Let’s say its 3000 watts or 3 kilo watts.

Ib(Design Current) = 3000 / 230 = 13amps

So, you would need a MCB or (BS EN 60898) with a rating of a minimum of 13 amps. A 16amp breaker could be used.

Once you understand this you can learn about derating cables and diversity.

I haven’t heard that 80% rule if I’m honest.

I would suggest buying a copy of the “Student's guide to the IET wiring regulations” it’s a great wee book and I’ve really enjoyed reading though it.
 
Your location shows as 'London', please could you confirm that's London, England? (It could be Ontario, CA!)

You mention ampacity, which is an American term not used in British english, and the 80% rule for continuous loads is also part of the USA's NEC which is their equivalent of our BS7671 wiring regs.

It sounds like you have been reading American sources, which although correct in themselves, will lead you astray when studying how we do things in the UK. There are quite different ways of achieving the same goals in different countries' regulations. What is correct in one place might be forbidden in another, like driving on the left hand side of the road.

FWIW as @TheConduitKing hints, there is sometimes more to working out Ib than dividing power by voltage. I=P/V works for resistive loads like heaters, but will be too low for inductive loads like induction motors, due to power factor. I won't bog you down in that for now, just be aware of it.
 

Reply to Work out breaker size? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Apologies up front but I'm a DIYer and only got 1 reply on that forum so trying here. I'm in Ontario Canada where a homeowner can do there own...
Replies
2
Views
869
Hi all I have a bench saw which is tripping a 100amp breaker on a workshop spread. The question i have is how does a D curve breaker work? I...
Replies
9
Views
1K
In a few days our local HVAC company will replace our propane furnace with a Mitsubishi heat pump (PUZ-HA42NKA1) and ducted air handler...
Replies
0
Views
2K
Hello all, I'm new to these forum so go easy on me! Apologies if this has been brought up many times before but I have some questions about...
Replies
4
Views
4K
I have 10 7.5A lights in a room on a breaker 10x7.5a=75a so 75a ÷ 230v is something crazy like 0.3A so what am I going to use a 1A breaker ...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock