- Reaction score
- 17,111
Spent yesterday morning running a spur in my kitchen from one double socket on the rfc to a new one along the same wall.
Original socket is just beside the multi gang grid switch for appliances. More on that later.
Wife came home from shopping with the birthday girl, ranted at me for not doing any dishes, as is typical, and proceeded to fill the dishwasher…. Which didn’t work.
Got the tools out again and started looking.
The original socket and spur both tested fine with 2 prong voltage detector first, then with ELI tester. 244v, but the socket for the dishwasher although also read 244, it wasn’t lighting up the 240 light on the 2 prong.
Was also giving a warning light on the ELI as power between N and PE.
Healthy would be
L to N yes
L to PE yes
N to E no
This surprised me as every other point on the same circuit was ok.
So although I hadn’t worked on it, I deduced the only solution was to look in the grid switch plate.
Lo and behold, pulled the grid forward and not one, but two neutrals popped out… the two legs from the ring on each end.
So, dishes done, and I’m back in the good books.
Although.
They went all the way to the Metrocentre and didn’t buy me anything!
Original socket is just beside the multi gang grid switch for appliances. More on that later.
Wife came home from shopping with the birthday girl, ranted at me for not doing any dishes, as is typical, and proceeded to fill the dishwasher…. Which didn’t work.
Got the tools out again and started looking.
The original socket and spur both tested fine with 2 prong voltage detector first, then with ELI tester. 244v, but the socket for the dishwasher although also read 244, it wasn’t lighting up the 240 light on the 2 prong.
Was also giving a warning light on the ELI as power between N and PE.
Healthy would be
L to N yes
L to PE yes
N to E no
This surprised me as every other point on the same circuit was ok.
So although I hadn’t worked on it, I deduced the only solution was to look in the grid switch plate.
Lo and behold, pulled the grid forward and not one, but two neutrals popped out… the two legs from the ring on each end.
So, dishes done, and I’m back in the good books.
Although.
They went all the way to the Metrocentre and didn’t buy me anything!
Last edited: