Discuss working length of circuit from resistance for volt drop in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
691
Hi all

could someone please be so kind to explain how i work out the length of a existing ring final circuit 2.5/1.5 T/E

and in turn Volt Drop

i know to work out length its L= R x 1000 divided by m/ohm/m but would i use the r1 measurement eg 0.58ohms
rn was 0.58ohms
r2 was 0.96
or from the highest measured value from step 2 cross connection of line and Neutral which is 0.33 ohms which was from a spur in the loft

any help would be appreciated think i am just confusing myself lol


to work length of circuit
is it
0.58x 1000 divided by 7.41
and then volt drop
0.58 x 2 x 1.2 x lenght divide 1000
cheers
 
Last edited:
2.5mm T&E ring.
1 conductor 2.5mm CSA @ 7.41mohm/m
1 conductor 1.5mm CSA @ 12.10mohm/m
{from page 166 OSG}

so your values give..
r1 @ 0.58/7.41 x 1000 = 78.27m
rn @ 0.58/7.41 x 1000 = 78.27m
r2 @ 0.96/12.10 x 1000 = 79.33m


That is how I work out the length Karl.

The Volt Drop mate is

Divide the length by 4 = approx 20 x 18 x 26/ 1000 = 9.36v

Bs 7671 pg 258, 6.1 correction for operating temp.

This calculation give you a ct of .923, x 9.36 = 8.36v

or

4 x 9.36 x 1000/26/18 = 98.3 / .923 = 85m

As I used approx 20 metres in the VD calc to round it up Karl you see it is ball park and if I used the percentage length of 78.27 it would have been closer

It assumes 20 amp at the furthest point and 12 amp distributed evenly around the ring so,

average = (32 + 20)/2 = 26






 
Last edited:
mate your a gent and should be a tutor lol as none i have learned with have explained this and the college course i am doing at minute for lv3 is the worst course i have done

i have been racking my brains to work it out can it be done from the measured impedence as the regs say
was using 32A as my Ib which you have corrected kindly most all sockets were around 0.29ohms apart from the spur to loft which was 0.33 for R1 +RN
thanks malc and tel who replied by pm
 
Malc jsut had a look at the relevent page you have mentioned in the regs

I wouldnt have been able to work it out from that mate lol that is one calc i am lost on i will copy your aswer for future reference

i had a feeling to work lenght from the resistance of the line ie r1 but didt kow to only allow 26A as my design current
 

Reply to working length of circuit from resistance for volt drop in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Replies
2
Views
2K
hi in college and watched some YouTube videos and read up on things I think I got the right formula but I'm not sure. Zsc= Zesc(or Zdbsc) +...
Replies
6
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi Guys I was asked to look at a twin extract fan system that was showing a trip fault after checking that both fans ran by temporarily bypassing...
Replies
8
Views
2K
So, for a bit of completely pointless fun really, does this antique looking item that was acquired entirely for novelty/aesthetics value work...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock