Discuss Working on live DC in the Industrial Electricians' Talk area at ElectriciansForums.net

F

froggy440

Hey guys,

My boss wants me terminating new supplies in a -48v d.c Distribution board. Easy enough but the board cannot be turned off due to critical load.

Now my question is this. Is it safe and or legal to work on live -48v d.c. and what would the consequences and dangers of possible short or electrocution?

Thanks!
-James
 
Hi - in my opinion it can be hazardous. The hazard I'm thinking about is vaporised metal caused by accidental short circuit. If the board has a low source impedance you will likely vaporise some metal if there is an accidental short. That can be very bad to be near. A proper RA should identify the risks, quantify and mitigate them. Safe isolation is the way to be, well, safe :)
 
no danger of electrocution but as said above, a short circuit could cause a serious flash over.
The consequence of electrocution would be a funeral followed by an investigation by health and safety .
do you mean checking that the coffin was lowerewd in accordance with strict H&S guidance. no steps used in the hole, scaffold and safety harnesses used correctly, filled in using plastic spades to avoid injury?
 
It can be legal, if done correctly.

The first thing to do is explore all possible options for isolating the supply, out of hours working or a planned shutdown.

Remember that if you do work live then the smallest slip could result in it all going off and you getting a face full of molten metal.

If isolation is not possible then a safe system of work needs to be planned and followed. This will likely include fully insulated tools and the use of temporary insulation and barriers.
 
It's a source of energy so the same methodology and RA is required as for live work at 230V. The risk of shock is lower (although not zero) but there is an added risk of complacency from thinking that the supply isn't 'really live'.
 
Any short circuit conditions will be spectacular and can result in injury or death, shocks are possible at 48volts but unlikely to be fatal. As mentioned live work only via a risk assessment and only by persons competant.
 
Hi,is this telecommunications or refinery,by any chance?
I would want to know,myself,the exact details,of why safe isolation is not possible,NOT having the details second-hand,boss or whatever.

I have had this scenario before,where the actual reason why safe isolation is allegedly "not possible",was down to the boss/clerk/contractor,not having a set of gonads,and being reticent regarding upsetting a client.
 

Reply to Working on live DC in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
653
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
Replies
21
Views
4K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
164
Hi all, After some help here. My boss at the company I work for is adamant that I must remove my electrical isolation, even though I don't deem...
Replies
23
Views
2K
Hi there. I’m hoping for some advice. I currently run a small limited company that provides IT services, both commercial and domestic so I...
Replies
0
Views
647

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock