wondering if anyone knows the best method of working something out:

if ive got a 3 phase supply, rated at 45Kva then how many amps do i have in total and per phase? does square root of 3 come into anywhere?
also be handy to have the above solved and equated into KW's as well :)

the above relates to commercial unit in leeds and this supply is what the shop has got.

cheers
 
mmmm feeling a bit thick today!! is the above formula gonna give me a wattage of
38277.2 or 38.3Kw? i used .85 as a pf but dont know if this is right, if someone could break down the above and give me amps per phase or total available amps and watts likewise that would be great!
 
mmmm feeling a bit thick today!! is the above formula gonna give me a wattage of
38277.2 or 38.3Kw? i used .85 as a pf but dont know if this is right, if someone could break down the above and give me amps per phase or total available amps and watts likewise that would be great!

well 45KVA is your apparant power, and is simply a product of supply volts by supply current

your watts (or KW) is your true power, and is a product of the supply current and v dropped accross the resistive element of the load

KVAR is your reactive power, and is current times v drop accroos reactive element of the load

of course, all this is theortical, using vectors etc etc

but what it means is your KW is smaller than your KVA

in fact true power / apparant power is p.f

so your p.f of o.85 x 45kVA = 38.25 KW

but of course, your loads may (or may not) be at 0.85 p.f

you should have your pf as high as possible, (close to unity), which means you are 'using' more of the KVA supplied

I have been in large installations running many inductive loads (motors etc) where they p.f correction capacitor banks fiited

anyway, lets say you have 38.25Kw

divide by three = 12.75Kw per phase divided by 230V (because its single phase) = 55.4 amps per phase

note this a very rough calc, and assumes perefctly balanced phases and loads, a fixed p.f of 0.85 etc etc

of course, your PF is not fixed

so using your 45KVA, divide by three = 15KVA per phase divide by 230V = 65A

this is 'available supply'

reality is, without a constantly chjanging p.f, so would your answer


oh, and i just made all that up because i am not an 'electrican' according to some on here:p
 
didnt see your post up there as well! thanks shakey.

yeah im getting simlar figures as well, so potentially if ive got a nicely balanced loading, with some evenly matched and as pure as poss on the pf, im looking at about 195A across all three phases.

motor wise, after talking to customer today he's getting some energy efficient single phase air con units, so hopefully they will have good pf as well as 10 refrigerators.

cheers for your response guys.

oh, and i just made all that up because i am not an 'electrican' according to some on here:p

lol! :) i hope it all sorts it self out n everybody becomes friends again!
 
just doing a load survey for me leeds job, just realised i was working it out wy wrong to begin with! i was doing 45000/400 and coming out with 112 or summat!! bit different to actually having 65a ish per phase!! lol
 
didnt see your post up there as well! thanks shakey.

yeah im getting simlar figures as well, so potentially if ive got a nicely balanced loading, with some evenly matched and as pure as poss on the pf, im looking at about 195A across all three phases.

motor wise, after talking to customer today he's getting some energy efficient single phase air con units, so hopefully they will have good pf as well as 10 refrigerators.

cheers for your response guys.

oh, and i just made all that up because i am not an 'electrican' according to some on here:p

lol! :) i hope it all sorts it self out n everybody becomes friends again!


hey no problems:p
 

Reply to working out Kva etc! in the Electricians' Talk | All Countries area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock