Discuss Wylex main switch in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
0
Hi , could someone help me please , I did an eicr yesterday. Few questions now
the ccu is the old Wylex board with push in type mcb's 3871 type , what is the main switch bs en number ? Can I say its a limitation as it's not evident ?

the Ze I recorded is 0.63 ohms it's a tncs , is this a c2 or c3 ?
 
the Ze I recorded is 0.63 ohms it's a tncs , is this a c2 or c3 ?

Seeing as it's almost double the stated max Ze value for a PME/TNC-S What code would you think it warrants!! In fact forget the code, get on to the local DNO and find out if they are happy with you're measured value!!
 
Yeah ring the good ol' DNO. Chances are you'll get some numpty on the other end not knowing what the hell you are on about!! That's after having gone through 6 or 7 different departments and clueless twits to boot!!
 

Reply to Wylex main switch in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hello, I have an old 16A Wylex SK type B plug-in breaker in the fuse box in my garage which keeps tripping, and every time (and only at that time)...
Replies
5
Views
2K
Hi guys. I was on EICR yesterday, where i found that the main earthing conductor is with very small csa- no more than 2.5cm2. Also they run the...
Replies
8
Views
3K
I currently have a Single Pole Double Throw switch with 5 pins (as shown below) which I want to wire up to UK mains: ┌─────┐ │...
Replies
9
Views
975
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
965

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock