Y Plan advice

Discuss Y Plan advice in the Central Heating Systems area at ElectriciansForums.net

stidge

-
Arms
Reaction score
50
Hi all, just after a bit of clarification please.
Ive fitted a danfoss dual channel programmer. Ive had to link L-1 and also using 1 as HW OFF, to GREY, on 3 port valve
Is that correct ?
Also pump use to be connected to ORANGE, but as ive had to add Pump overrun from boiler,ive connected PUMP/ boiler direct to PUMP as the overrun would be firing boiler all the time ? Cheers for any help
 
You've linked permanent live to 1, and Grey on the valve is to 1 too?
You'll probably have to get rid of the live link from L to 1.
The pump over-run should be run from the 'pump over-run' output on the boiler, it should not be connected to orange on the valve.
Download the wiring diagram, and follow it closely.
 
Last edited by a moderator:
Hi all, just after a bit of clarification please.
Ive fitted a danfoss dual channel programmer. Ive had to link L-1 and also using 1 as HW OFF, to GREY, on 3 port valve
Is that correct ?
Also pump use to be connected to ORANGE, but as ive had to add Pump overrun from boiler,ive connected PUMP/ boiler direct to PUMP as the overrun would be firing boiler all the time ? Cheers for any help
At a guess regarding your programmer, this may, or may not, help
 

Attachments

  • Y-Plan-Biflow-Wiring-Diagram-300x270.png
    12.4 KB · Views: 110
I think the drawing I stuck up seems like the right one after looking at his OP again, it all seems to fit in, the colours are the same as is the programmer numbers, the only difference is the link missing but thats no big deal and easily sorted.
 
Ok Leo even though it says to link in diagram ? Cheers

The wiring diagram of an LP522 does not say to link L to 1, unless they've put the wrong sticker on the back of it?
The terminals from left to right are:
Neutral
Live
1 - dhw off
2 - ch off
3 - dhw on
4 - ch on

The single channel version has a volt free output so would need a link from L to 1 for normal 240V operation.
 
little tip.I keep the drawings as above in a plastic wallet in the van door. It helps a lot for the various wiring plans to follow them.
Actually a good idea, that said after a while you won't need a drawing if connecting up heating systems regularly, but good advice netherless fella
 

Reply to Y Plan advice in the Central Heating Systems area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top