Hi im wiring a y plan heating system which ive done before a few times but cant seem to get my head around it. A few questions really. Q1 does boiler supply come from wiring centre with fcu close by or need its own circuit from c.u. via fcu. Can wiring centre come from fcu of ring circuit (would that be ok to bs7671) And am i right in thinking the cylinder needs its own supply from cu via 20a dp switch. Sorry long day brain just wont work.
 
ahh thanks guys thought i was on right track. and thanks dan got that diagram but it confused me. LNE to boiler from wiring centre thats fine but isnt the switched live missing. i was thinking i would need to have at least a 3 core and earth cable to boiler am i right in saying that.
 
oops i mean 5 core LNE. hot water switch wire central heating switch wire. Connected inside boiler also doesnt show that on diagram or am i being a complete plank. Sorry got to price for this tommorow.
 
As a minimum I'd recommend a 4 cores, this will give you a permanent live, a switched live a neutral & an earth.

Check boiler instructions regarding circulation pump as if it is external to the boiler you may need a cable from the boiler to the pump as some boilers control the pump directly rather than via the wiring centre.

Only one switched live to the boiler from the wiring centre will be needed as both CH & HW use the same one.
 
thats what i was thinking and am going to do. I got it now brain finally working. Thanks all who helped me there. Sometimes just need to chat about it to see the light...............
 

Reply to y plan heating system in the Australia area at ElectriciansForums.net

Similar Threads

I had to wire in an extra 2 port valve today to protect a newly installed unvented cylinder (replacing the old gravity fed one) in a standard Y...
Replies
12
Views
2K
Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K
Hello Guys, I was wondering if any of you nice chaps could lend me some advice. So I have an open vented heating system with a 3 port valve...
Replies
11
Views
2K
I have not had to do the wiring for a wet underfloor heating system before. I think I started a thread fairly recently and had some very good...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock