Well-spotted NDG. The tester has inputted 60497-3 on site instead of 60947-3 and the error wasn't picked-up by his boss when he supposedly checked the form.

From what I've learned about the company concerned, it is apparent that they are a one-stop "landlord compliance" service who offer not only electrical certification, but gas certification too. On their website they say that they:

provide certification services to landlords and letting agencies including PAT testing, EICR, gas safety, legionnaires assessment, smoke alarm testing and fitting.

And:

We will liaise directly with your tenants, carry out the work to the highest standards and all certification will be completed electronically and available same day to access and download any new or archived certificates at any point from your client login area.

However, the extremely poor quality of this EICR makes a complete mockery of the claim that they "carry out the work to the highest standards".

They continue:

We prove all certificates required to be fully compliant. Fast efficient service with documents available online within hours of the inspection. We can fully manage all your portfolio of properties or a simple buy as required service.

I'm quite certain that this was a 'let's get this report done as quickly as possible so we can get to our next job as we've got another five EICRs to do today so we can meet our target and avoid the boss' wrath type of job. The property, incidentally, is a three-bedroom flat. My fee for that would be £165.00. This is about as much as the over-saturated market will pay up here. A big factor in why prices for EICRs are so low in Glasgow is largely down to the dubious practices of companies such as the one who did this report. But you get what you pay for in the end.
 
My observations:

1. The form used is the 2008 version. The tester should have used the current 2018 version.

2. The installation is said to have been "100% tested". If so, then why has the schedule of tests been left blank?

3. The summary of the condition of the installation has been left blank. Why?

4. Mandatory inspection and testing of private rented accommodation in Scotland takes place every five years, not three as is stated on the report.

5. The nominal voltage of the installation is stated to be 239 volts. I would normally attribute an error like this to a typo, but given the other glaring errors that I've noticed on this report I'm not sure that this actually is a typo.

6. The maximum demand check-box has been marked N/A. Sloppy.

7. Main protective bonding to gas and water services is stated to be present. If so, then why has the property owner been quoted for "materials to install main gas bond"? Furthermore, why has the tester quoted for a 16mm conductor when 10mm would suffice?

8. Section 3.1, all parts relating to main protective bonding have been marked as satisfactory. But how can this possibly be so when the property owner has been told that part of the remedial works concerns the installation of bonding to the gas service? Which of these two contradictory statements is true and which is false?

9. Although the earthing system has been marked as being TN-C-S in section 5.12, RCD(s) provided for fault protection has nevertheless been checked. Some mistake surely!

10. Section 5.16, presence of RCD restest notice, has been marked as N/A. Another glaring error.

11. Giving C3 codes for the items listed in sections 5.20 and 5.21 is bordering on the ridiculous. It would be quicker just to affix the missing labels. Ditto section 6.1. Giving a code for unsleeved switched lives is unwarranted IMHO.

12. Section 6.9, presence and adequacy of circuit protective conductors has been marked as satisfactory. However, under the Schedule of Items Tested, it is stated that continuity of protective conductors requires further investigation. Why the contradiction?

13. The Test Results and Circuit Details section contain no data other than multiple entries in the Zs column of 0.17. Since the report was supposedly checked before being signed-off by the tester's boss, there really are no excuses for the extremely poor quality of this EICR. None whatsoever.

Then there are the codes. In my opinion, items 1, 2 and 3 do not merit codes. I'm puzzled as to why a faulty socket merits a C2 while a faulty FCU merits a C3.

The description given for item 7 would make more sense if the tester had stated which circuit he believed to be overloaded.

Item 8 isn't something I would code unless something drastic had occurred such as wetpants installing a boiler directly in front of the consumer unit.

Had the tester bothered to list the actual readings obtained from his IR tests we might then know the identity of which "2 x separate circuits" he's referring to regarding item 9.

As for item 10, all I can say here is WTF? If the kitchen sockets aren't on a ring then they must be on a radial and vice-versa. I would expect to hear such a ridiculous statement from a plumber or a kitchen-fitter, but never from someone claiming to be an electrician.

I'm utterly embarrassed to reveal that the company responsible for this report are SELECT members. My advice to the property owner will be that he should either refuse to pay for this EICR, or obtain a refund as the report isn't worth the paper that it's printed on. I would also advise that the installation be retested by a reputable contractor so that its true condition may be ascertained. I would further advise the property owner to make a complaint to SELECT whom I'm sure will be aghast.
I suspect that your summing up of the report took longer to do than the report itself.
 
I have just done an EICR , I waved my note book at the consumer unit , poked my head round a few doors did i mention I left my tester in the van but no matter I know what the readings will be anyway.
I am going to scribble some notes on my test sheets , tick a few boxes at random as you do and head down the pub for lunch.
£195 cash in my pocket for 45mins work.

Am I doing this right ???
 
I have just done an EICR , I waved my note book at the consumer unit , poked my head round a few doors did i mention I left my tester in the van but no matter I know what the readings will be anyway.
I am going to scribble some notes on my test sheets , tick a few boxes at random as you do and head down the pub for lunch.
£195 cash in my pocket for 45mins work.

Am I doing this right ???
Don't worry Dusty, you'll soon get faster with some experiance.
 
I have just done an EICR , I waved my note book at the consumer unit , poked my head round a few doors did i mention I left my tester in the van but no matter I know what the readings will be anyway.
I am going to scribble some notes on my test sheets , tick a few boxes at random as you do and head down the pub for lunch.
£195 cash in my pocket for 45mins work.

Am I doing this right ???
No you should be doing it from your van.
 
4. Mandatory inspection and testing of private rented accommodation in Scotland takes place every five years, not three as is stated on the report.
Much of what you point out is valid, however I will have to disagree on this point. Regardless of whether the legal requirement is for these to be carried out five-yearly or not, the Report must surely state a recommendation to next inspection based upon the condition of the electrical installation. Otherwise the box would be pointless.

So if the condition of the installation warranted the advice of three years to the next inspection, then that is the interval that should be stated. Or if it was in really bad condition then perhaps six months or whatever. I have had this issue before with business owners complaining that I had not given a five year recommendation for their business premises. I pointed out that my assessment was based on the installation as inspected - as it is required to be.
 

Reply to Yet Another Dodgy EICR in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The buyer of my house has had an EICR done. I have anonymized and attached. Also the associated quote for remediation. I am wondering: surely...
Replies
26
Views
3K
I commissioned an EICR to be done on a property that is in Wales as this is now a requirement in order to let on any new tenancies after 1st...
Replies
1
Views
2K
Agent contacts me with an urgent request for a CU upgrade in Camden. They send over an EICR done the previous month and I have a quick skim. All...
Replies
99
Views
10K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Next door neighbour .Single mother 2 young kids . Been there 6-7 years .landlady is super reluctant to ever communicate no matter what the issue ...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock