Search the forum,

Discuss Yet Another Dodgy EICR in the UK Electrical Forum area at ElectriciansForums.net

JK-Electrical

-
Esteemed
Arms
Reaction score
1,536
A prospective customer has contacted me via a recommendation received from a mutual contact and asked me to provide a quotation for remedial works that have arisen from an EICR that was recently undertaken at a three-bedroom property he rents out. In his initial e-mail, he said that the letting agent has told him that the following remedial works are necessary:

Replace Fusebox then test and certify
Materials to replace a double socket
Materials to install main gas bond, 10m of 16mm earth cable, 2 bonding clamps

I asked the property owner to forward me a copy of the EICR. I have redacted all personal details contained therein and have uploaded the report for your consideration, scrutiny and appraisal. My own personal assessment is that the property owner has been ripped-off by a drive-by tester and that the report isn't worth the paper that it's written on. Although the property owner was charged just £95.00 by the letting agent, even this amount could be considered excessive given the poor quality of the report.

Over to you guys .....
 

Attachments

  • EICR-edited.pdf
    309.8 KB · Views: 390
Last edited:
Points 9 and 10 are strange to say the least. If the kitchen sockets are not a ring/radial what are they? Or am i missing something
According to the test schedule, there is no circuit for the kitchen sockets. Indeed, according to the test schedule there are no circuits anywhere in the installation ..... all of which are stated to have a Zs of 0.17 ohms!o_O
 
That's how I'm gonna start filling in the test results from now on! What a time saver it will be!
I didn't find the list of observations too offensive TBH. Could have been worded better but have seen worse. But without the test results surely it's just a visual ?!
 
But without the test results surely it's just a visual ?!

Although the tester has stated that the installation was "100% tested", the absence of any test results casts a long shadow of doubt as to whether he actually did carry-out a full range of tests on every circuit. This report isn't fit for the purpose as without the test results it's utterly useless as it tells us nothing about the overall condition of the installation.
 
My observations:

1. The form used is the 2008 version. The tester should have used the current 2018 version.

2. The installation is said to have been "100% tested". If so, then why has the schedule of tests been left blank?

3. The summary of the condition of the installation has been left blank. Why?

4. Mandatory inspection and testing of private rented accommodation in Scotland takes place every five years, not three as is stated on the report.

5. The nominal voltage of the installation is stated to be 239 volts. I would normally attribute an error like this to a typo, but given the other glaring errors that I've noticed on this report I'm not sure that this actually is a typo.

6. The maximum demand check-box has been marked N/A. Sloppy.

7. Main protective bonding to gas and water services is stated to be present. If so, then why has the property owner been quoted for "materials to install main gas bond"? Furthermore, why has the tester quoted for a 16mm conductor when 10mm would suffice?

8. Section 3.1, all parts relating to main protective bonding have been marked as satisfactory. But how can this possibly be so when the property owner has been told that part of the remedial works concerns the installation of bonding to the gas service? Which of these two contradictory statements is true and which is false?

9. Although the earthing system has been marked as being TN-C-S in section 5.12, RCD(s) provided for fault protection has nevertheless been checked. Some mistake surely!

10. Section 5.16, presence of RCD restest notice, has been marked as N/A. Another glaring error.

11. Giving C3 codes for the items listed in sections 5.20 and 5.21 is bordering on the ridiculous. It would be quicker just to affix the missing labels. Ditto section 6.1. Giving a code for unsleeved switched lives is unwarranted IMHO.

12. Section 6.9, presence and adequacy of circuit protective conductors has been marked as satisfactory. However, under the Schedule of Items Tested, it is stated that continuity of protective conductors requires further investigation. Why the contradiction?

13. The Test Results and Circuit Details section contain no data other than multiple entries in the Zs column of 0.17. Since the report was supposedly checked before being signed-off by the tester's boss, there really are no excuses for the extremely poor quality of this EICR. None whatsoever.

Then there are the codes. In my opinion, items 1, 2 and 3 do not merit codes. I'm puzzled as to why a faulty socket merits a C2 while a faulty FCU merits a C3.

The description given for item 7 would make more sense if the tester had stated which circuit he believed to be overloaded.

Item 8 isn't something I would code unless something drastic had occurred such as wetpants installing a boiler directly in front of the consumer unit.

Had the tester bothered to list the actual readings obtained from his IR tests we might then know the identity of which "2 x separate circuits" he's referring to regarding item 9.

As for item 10, all I can say here is WTF? If the kitchen sockets aren't on a ring then they must be on a radial and vice-versa. I would expect to hear such a ridiculous statement from a plumber or a kitchen-fitter, but never from someone claiming to be an electrician.

I'm utterly embarrassed to reveal that the company responsible for this report are SELECT members. My advice to the property owner will be that he should either refuse to pay for this EICR, or obtain a refund as the report isn't worth the paper that it's printed on. I would also advise that the installation be retested by a reputable contractor so that its true condition may be ascertained. I would further advise the property owner to make a complaint to SELECT whom I'm sure will be aghast.
 
Although the tester has stated that the installation was "100% tested", the absence of any test results casts a long shadow of doubt as to whether he actually did carry-out a full range of tests on every circuit. This report isn't fit for the purpose as without the test results it's utterly useless as it tells us nothing about the overall condition of the installation.

I was being tongue in cheek there JK. I agree that it is not worth the paper it is written on at all, and this should not be paid for at all The schedule of test results is the main page we go to I would say for 'useful' information about an installation. Doesn't the 'tester' say something about low IR in the observations as well...! Low IR where !

And do sparks in Scotland use a different main switch? I use 60947-3 type usually !!
 
Well-spotted NDG. The tester has inputted 60497-3 on site instead of 60947-3 and the error wasn't picked-up by his boss when he supposedly checked the form.

From what I've learned about the company concerned, it is apparent that they are a one-stop "landlord compliance" service who offer not only electrical certification, but gas certification too. On their website they say that they:

provide certification services to landlords and letting agencies including PAT testing, EICR, gas safety, legionnaires assessment, smoke alarm testing and fitting.

And:

We will liaise directly with your tenants, carry out the work to the highest standards and all certification will be completed electronically and available same day to access and download any new or archived certificates at any point from your client login area.

However, the extremely poor quality of this EICR makes a complete mockery of the claim that they "carry out the work to the highest standards".

They continue:

We prove all certificates required to be fully compliant. Fast efficient service with documents available online within hours of the inspection. We can fully manage all your portfolio of properties or a simple buy as required service.

I'm quite certain that this was a 'let's get this report done as quickly as possible so we can get to our next job as we've got another five EICRs to do today so we can meet our target and avoid the boss' wrath type of job. The property, incidentally, is a three-bedroom flat. My fee for that would be £165.00. This is about as much as the over-saturated market will pay up here. A big factor in why prices for EICRs are so low in Glasgow is largely down to the dubious practices of companies such as the one who did this report. But you get what you pay for in the end.
 
My observations:

1. The form used is the 2008 version. The tester should have used the current 2018 version.

2. The installation is said to have been "100% tested". If so, then why has the schedule of tests been left blank?

3. The summary of the condition of the installation has been left blank. Why?

4. Mandatory inspection and testing of private rented accommodation in Scotland takes place every five years, not three as is stated on the report.

5. The nominal voltage of the installation is stated to be 239 volts. I would normally attribute an error like this to a typo, but given the other glaring errors that I've noticed on this report I'm not sure that this actually is a typo.

6. The maximum demand check-box has been marked N/A. Sloppy.

7. Main protective bonding to gas and water services is stated to be present. If so, then why has the property owner been quoted for "materials to install main gas bond"? Furthermore, why has the tester quoted for a 16mm conductor when 10mm would suffice?

8. Section 3.1, all parts relating to main protective bonding have been marked as satisfactory. But how can this possibly be so when the property owner has been told that part of the remedial works concerns the installation of bonding to the gas service? Which of these two contradictory statements is true and which is false?

9. Although the earthing system has been marked as being TN-C-S in section 5.12, RCD(s) provided for fault protection has nevertheless been checked. Some mistake surely!

10. Section 5.16, presence of RCD restest notice, has been marked as N/A. Another glaring error.

11. Giving C3 codes for the items listed in sections 5.20 and 5.21 is bordering on the ridiculous. It would be quicker just to affix the missing labels. Ditto section 6.1. Giving a code for unsleeved switched lives is unwarranted IMHO.

12. Section 6.9, presence and adequacy of circuit protective conductors has been marked as satisfactory. However, under the Schedule of Items Tested, it is stated that continuity of protective conductors requires further investigation. Why the contradiction?

13. The Test Results and Circuit Details section contain no data other than multiple entries in the Zs column of 0.17. Since the report was supposedly checked before being signed-off by the tester's boss, there really are no excuses for the extremely poor quality of this EICR. None whatsoever.

Then there are the codes. In my opinion, items 1, 2 and 3 do not merit codes. I'm puzzled as to why a faulty socket merits a C2 while a faulty FCU merits a C3.

The description given for item 7 would make more sense if the tester had stated which circuit he believed to be overloaded.

Item 8 isn't something I would code unless something drastic had occurred such as wetpants installing a boiler directly in front of the consumer unit.

Had the tester bothered to list the actual readings obtained from his IR tests we might then know the identity of which "2 x separate circuits" he's referring to regarding item 9.

As for item 10, all I can say here is WTF? If the kitchen sockets aren't on a ring then they must be on a radial and vice-versa. I would expect to hear such a ridiculous statement from a plumber or a kitchen-fitter, but never from someone claiming to be an electrician.

I'm utterly embarrassed to reveal that the company responsible for this report are SELECT members. My advice to the property owner will be that he should either refuse to pay for this EICR, or obtain a refund as the report isn't worth the paper that it's printed on. I would also advise that the installation be retested by a reputable contractor so that its true condition may be ascertained. I would further advise the property owner to make a complaint to SELECT whom I'm sure will be aghast.
I suspect that your summing up of the report took longer to do than the report itself.
 
I have just done an EICR , I waved my note book at the consumer unit , poked my head round a few doors did i mention I left my tester in the van but no matter I know what the readings will be anyway.
I am going to scribble some notes on my test sheets , tick a few boxes at random as you do and head down the pub for lunch.
£195 cash in my pocket for 45mins work.

Am I doing this right ???
 
I have just done an EICR , I waved my note book at the consumer unit , poked my head round a few doors did i mention I left my tester in the van but no matter I know what the readings will be anyway.
I am going to scribble some notes on my test sheets , tick a few boxes at random as you do and head down the pub for lunch.
£195 cash in my pocket for 45mins work.

Am I doing this right ???
Don't worry Dusty, you'll soon get faster with some experiance.
 
I have just done an EICR , I waved my note book at the consumer unit , poked my head round a few doors did i mention I left my tester in the van but no matter I know what the readings will be anyway.
I am going to scribble some notes on my test sheets , tick a few boxes at random as you do and head down the pub for lunch.
£195 cash in my pocket for 45mins work.

Am I doing this right ???
No you should be doing it from your van.
 
4. Mandatory inspection and testing of private rented accommodation in Scotland takes place every five years, not three as is stated on the report.
Much of what you point out is valid, however I will have to disagree on this point. Regardless of whether the legal requirement is for these to be carried out five-yearly or not, the Report must surely state a recommendation to next inspection based upon the condition of the electrical installation. Otherwise the box would be pointless.

So if the condition of the installation warranted the advice of three years to the next inspection, then that is the interval that should be stated. Or if it was in really bad condition then perhaps six months or whatever. I have had this issue before with business owners complaining that I had not given a five year recommendation for their business premises. I pointed out that my assessment was based on the installation as inspected - as it is required to be.
 
Much of what you point out is valid, however I will have to disagree on this point. Regardless of whether the legal requirement is for these to be carried out five-yearly or not, the Report must surely state a recommendation to next inspection based upon the condition of the electrical installation. Otherwise the box would be pointless.

So if the condition of the installation warranted the advice of three years to the next inspection, then that is the interval that should be stated. Or if it was in really bad condition then perhaps six months or whatever. I have had this issue before with business owners complaining that I had not given a five year recommendation for their business premises. I pointed out that my assessment was based on the installation as inspected - as it is required to be.

I understand and would not normally take issue with what you say. However, in this particular instance I seriously doubt that an installation which the tester has assessed as being only 15 years old would require periodic testing at three-year intervals. Fifty years, perhaps, yes. Fifteen, no. Not unless the installation was in unusually poor condition for its age. But in the absence of any test results we have no way of determining if this is actually the case here.
 
Out of curiosity, what would you guys usually charge for undertaking an EICR in a three-bedroom property?
 
According to a landlord customer of mine £65. Can I beat that price she has been quoted ? :laughing:

Yes of course madam , and I will drive past tonight and compile my report this evening. I won’t even have to disturb the tenants.
It will be with you via email at 9am tomorrow morning

Please deposit £64 into this bank account
 
I remember when I was an apprentice you could get a pir done at £4 per circuit

That was 2o years ago thou
 
I've just quoted a private landlord £250, it's a 3 bed house. I always explain that I have to be thorough as it's important and need a day to do it right including the paperwork. Accepted immediately. :) But in that price we'd replace the odd damaged socket or light switch for example and if we complete the job in say 6 hours I'll knock a little bit off the quoted cost, they like that.
 
I've just quoted a private landlord £250, it's a 3 bed house. I always explain that I have to be thorough as it's important and need a day to do it right including the paperwork. Accepted immediately. :) But in that price we'd replace the odd damaged socket or light switch for example and if we complete the job in say 6 hours I'll knock a little bit off the quoted cost, they like that.

And the screw heads would be lined up :):)
 
According to a landlord customer of mine £65. Can I beat that price she has been quoted ? :laughing:
I've just quoted a private landlord £250, it's a 3 bed house. I always explain that I have to be thorough as it's important and need a day to do it right including the paperwork. Accepted immediately. :) But in that price we'd replace the odd damaged socket or light switch for example and if we complete the job in say 6 hours I'll knock a little bit off the quoted cost, they like that.

£250.00 sounds about right Dave. Alas, it just isn't possible to get anywhere near that kind of price accepted around Glasgow, not when you have "landlord compliance certification" companies offering to do EICRs in three-bedroom properties for £95.00.

I'm considering withdrawing EICRs from the list of services that I offer and withdrawing from this saturated market altogether as it's become a race to the bottom.
 
£250.00 sounds about right Dave. Alas, it just isn't possible to get anywhere near that kind of price accepted around Glasgow, not when you have "landlord compliance certification" companies offering to do EICRs in three-bedroom properties for £95.00.

I'm considering withdrawing EICRs from the list of services that I offer and withdrawing from this saturated market altogether as it's become a race to the bottom.

To be honest I don't get quite a few mate, the accepted ones are generally existing customers or someone that I've been recommended to. But I'd say there's a major problem right across the country with bad EICRs, I see plenty just as bad as the one you've recently highlighted. It's never right when you're undercut by these unscrupulous idiots who couldn't care less, not sure what we can really do about it though.... :(
 
To be honest I don't get quite a few mate, the accepted ones are generally existing customers or someone that I've been recommended to. But I'd say there's a major problem right across the country with bad EICRs, I see plenty just as bad as the one you've recently highlighted. It's never right when you're undercut by these unscrupulous idiots who couldn't care less, not sure what we can really do about it though.... :(

Some of the EICRs that I've been asked to provide a second opinion on have either turned-out to be fake, or incorrect due to the tester's incompetence. If what I've witnessed up here in Glasgow is typical of the rest of the UK, then yes, we most certainly do have a major problem on our hands.

As honest, professional electricians all we can do is identify and expose unscrupulous operators wherever we find them.
 
Last edited:
Out of curiosity, what would you guys usually charge for undertaking an EICR in a three-bedroom property?
£200 is my starting price for them, i.e. I don't do them for less than that.

So with a standard three bed generally the £200.

I personally feel the base price should be £250 to allow for a day but I've found that I can regularly get them accepted at £200 but £250 not so much so. That said, add a bedroom or power in a garage or shed or whatever and it would be £250 upwards.
 
Which makes a complete mockery of the mandatory EICRs for rented properties in Scotland and coming to England at some point. It just becomes a box ticking exercise to be done at the lowest cost possible.
You’re absolutely right Simon although you didn’t mention WALES! The EICR now just seems to be pages of tick boxes the worst part is that I do EICR’s for private landlords and then don’t get called back to rectify problems I don’t know if it’s because I find so many problems and give accurate price to reflect their neglect of electrics over the years or if they want me to summarise the faults and then get a cheap sparky/diyer in to do botch jobs and get certificate from elsewhere won’t believe some of the stuff I’ve come across
 
Which makes a complete mockery of the mandatory EICRs for rented properties in Scotland and coming to England at some point. It just becomes a box ticking exercise to be done at the lowest cost possible.
My sentiments exactly.
My estimation of 90% of eicrs falling well below what should be regarded as acceptable,it may not be far off the mark
On the basis of what I've seen with my own eyes, I wouldn't disagree with your estimation.
Rouge companies who have destroyed the market with insane pricing whilst employing people with too little experience for the task
You have succinctly hit the nail on the head. Well said Des.
 
@JK-Electrical Have you reported this to SELECT? I'm NICEIC but have to say my recent contact with them over poor work I found was exceptional even though the culprit wasn't registered with any CPS (or SJIB) and I'm not in the SELECT gang. In contrast the NICEIC were appalling.
 
@JK-Electrical Have you reported this to SELECT?
I most certainly have Richy. SELECT have been informed, and the company responsible for this poor-quality EICR will hopefully be disciplined, or better still, have their membership revoked. I sure hope so.
I'm NICEIC but have to say my recent contact with them over poor work I found was exceptional even though the culprit wasn't registered with any CPS (or SJIB) and I'm not in the SELECT gang. In contrast the NICEIC were appalling.
We will never be able to raise industry standards if we bury our heads in the sand, shrug our shoulders and say it isn't our problem. It is our problem! It's our industry!! Not only are these rogue companies compromising electrical safety in other people's properties, they are also compromising the livelihoods of conscientious contractors who can provide a more professional service, but who are prevented from doing so because they cannot compete with the ridiculously low prices that these rogue "landlord certification" companies submit.

I don't know what state the domestic market is in up in your neck of the woods, but down here in Glasgow the market is in very bad shape indeed. While I have come to expect poor quality workmanship from the plumbers, kitchen-fitters, bathroom-fitters and DIYers who carry-out electrical installation work, I do not, however, expect to see the same from a SELECT member. They bring discredit upon the good name of SELECT. I therefore had no reservations whatsoever in reporting the company concerned.
 
Totally agree @JK-Electrical in my area there is me and 1 SELECT guy who are registered but we have to compete with another 12 dangerous Dave's, Brian the bodgers and now the super wizz-kid that's done his 3 week course!

Thing is if all the CPS companies were genuinely interested in raising standards then they could see all these people as potential new members and thus much more revenue. Problem with the NICEIC is they dont give a ---- unless you are falsely using their logo. Anything else falls on deaf ears. The NICEIC have a roadshow in Inverness soon so I shall be having my voice if I can.

My business is lucky as we do a lot of renewables and commercial work but we do also benefit off these 'bottom feeders' by being called in to fix their faults. Its money for the business but I always feel bad for the customer as they shouldn't have to pay twice. Most are ignorant about competency, qualifications etc.

Only last night a hotel called saying their 'local electrician' couldn't attend an emergancy (no bedroom lights) until sunday. They wanted me to go. 18 months ago I put right this 'local electricians' work as part of an EICR and it cost the hotel a huge amount of cash. But even then they haven't learned anything from it. I suggested they call somebody out from Inverness which is a 2 hour drive each way! I had beer to drink :)

Roll on the Scottish government giving us protected title. Maybe then a body (SELECT) can get some real teeth and kick these people out of the industry (I can live in hope).
 
Totally agree @JK-Electrical in my area there is me and 1 SELECT guy who are registered but we have to compete with another 12 dangerous Dave's, Brian the bodgers and now the super wizz-kid that's done his 3 week course!

Thing is if all the CPS companies were genuinely interested in raising standards then they could see all these people as potential new members and thus much more revenue. Problem with the NICEIC is they dont give a **** unless you are falsely using their logo. Anything else falls on deaf ears. The NICEIC have a roadshow in Inverness soon so I shall be having my voice if I can.

My business is lucky as we do a lot of renewables and commercial work but we do also benefit off these 'bottom feeders' by being called in to fix their faults. Its money for the business but I always feel bad for the customer as they shouldn't have to pay twice. Most are ignorant about competency, qualifications etc.

Only last night a hotel called saying their 'local electrician' couldn't attend an emergancy (no bedroom lights) until sunday. They wanted me to go. 18 months ago I put right this 'local electricians' work as part of an EICR and it cost the hotel a huge amount of cash. But even then they haven't learned anything from it. I suggested they call somebody out from Inverness which is a 2 hour drive each way! I had beer to drink :)

Roll on the Scottish government giving us protected title. Maybe then a body (SELECT) can get some real teeth and kick these people out of the industry (I can live in hope).

You'd think that wouldn't you? I mean just the other day there was a local woman in crown court having falsely claimed to be Gas Safe registered, why we haven't got a central body like thar, and the legal regulation to be registered God only knows.
 
I was in Helensburgh yesterday (for those south of the border it is a seaside town on the Clyde) collecting my car after a service and MOT. It was a £700 bill, but i trust my mechanic completely, and was happy with his charges as I know my car is as safe as it can be after his ministrations.
Anyway, while i was chatting to him, a van drew up...a local electrician...turns out he spemds most of his time sorting out bodged jobs in the local area...he doesn't like the bodges, but he loves the work he gets fixing them. So sad that he is always second in line...but sadder still that he is so busy with such work. Helensburgh is a fairly posh place, with many huge old houses, and plenty of money, so also sad that those rich folk go for cut-price "electricians"...
 
Anyway, while i was chatting to him, a van drew up...a local electrician...turns out he spemds most of his time sorting out bodged jobs in the local area...he doesn't like the bodges, but he loves the work he gets fixing them. So sad that he is always second in line...but sadder still that he is so busy with such work. Helensburgh is a fairly posh place, with many huge old houses, and plenty of money, so also sad that those rich folk go for cut-price "electricians"...

As you already know, my seafaring, rum-guzzling, plundering friend, I too have spent a considerable amount of tine putting right lash-ups. However, unlike the Helensburgh spark, I derive no pleasure whatsoever from this type of work. I find it tedious.

The clowns who create these lash-ups will continue to thrive at the expense of bona fide contractors until such times as The SNP regime through in Edinburgh takes its finger out of its arse and passes legislation that will give Scottish electricians protection of title.
 
Totally agree @JK-Electrical in my area there is me and 1 SELECT guy who are registered but we have to compete with another 12 dangerous Dave's, Brian the bodgers and now the super wizz-kid that's done his 3 week course!

Thing is if all the CPS companies were genuinely interested in raising standards then they could see all these people as potential new members and thus much more revenue. Problem with the NICEIC is they dont give a **** unless you are falsely using their logo. Anything else falls on deaf ears. The NICEIC have a roadshow in Inverness soon so I shall be having my voice if I can.

My business is lucky as we do a lot of renewables and commercial work but we do also benefit off these 'bottom feeders' by being called in to fix their faults. Its money for the business but I always feel bad for the customer as they shouldn't have to pay twice. Most are ignorant about competency, qualifications etc.

Only last night a hotel called saying their 'local electrician' couldn't attend an emergancy (no bedroom lights) until sunday. They wanted me to go. 18 months ago I put right this 'local electricians' work as part of an EICR and it cost the hotel a huge amount of cash. But even then they haven't learned anything from it. I suggested they call somebody out from Inverness which is a 2 hour drive each way! I had beer to drink :)

Roll on the Scottish government giving us protected title. Maybe then a body (SELECT) can get some real teeth and kick these people out of the industry (I can live in hope).

Protection of title is coming Richy. It's a question of when rather than if. But protection of title on its own isn't enough, in my opinion. The public needs to be educated about electricians, the work we do and the standards we work to. How this could be achieved in actuality, I'm not sure.
 
Protection of title is coming Richy. It's a question of when rather than if. But protection of title on its own isn't enough, in my opinion. The public needs to be educated about electricians, the work we do and the standards we work to. How this could be achieved in actuality, I'm not sure.
What scares me about any licencing scheme or title protection is which organisations will get their mitts on having the say as to what constitutes an electrician, levels of qualification and so on. The govt is likely to take the recommendations of whoever is shouting loudest, and that is very likely to be those who have most to gain by keeping skills down and labour cheap.
 
There's a saying that you should be careful what you wish for. When the BC notification rules came in, everyone (well, many) thought it would cure many ills - while in practice it just drove a lot of bodging underground, created more BIY, and created a whole new sales pitch for the charlatans.
It was clearly recognised or they wouldn't have relaxed the requirements a few years later.
So what is the protected title likely to mean in practice ? Membership of a scheme ? Yeah, we all know how much that guatantees quality of work :rolleyes: Certain qualifications ? The bar would need to be fairly low or you create a shortage which then promotes BIY and dodgy underground work.
Personally I don't think that is whete the problem lies, rather it relies on general ignorance amongst the public, and lack of any meaningful enforcement against the bodgers due to the limitef rrsources of Trading Standards.
 
What scares me about any licencing scheme or title protection is which organisations will get their mitts on having the say as to what constitutes an electrician, levels of qualification and so on. The govt is likely to take the recommendations of whoever is shouting loudest, and that is very likely to be those who have most to gain by keeping skills down and labour cheap.

When protection of title is eventually introduced it will apply only to electricians who are based in Scotland. My information is that a database containing the details of all registered electricians in Scotland will be built and be administered by SELECT, NICEIC and the SJIB. NICEIC were initially opposed to the proposal but are now fully on board. Only those electricians who hold appropriate, up to date qualifications will be eligible for inclusion on the database. If your name isn't on the database and you as much as even advertise yourself as an electrician you will be committing a criminal offence. My understanding is that electricians whose qualifications are inadequate or have lapsed will be given a time-limited opportunity to get up to speed.

NICEIC Domestic Installers and those who have entered the industry via short courses will have to invest heavily to achieve the recognised level of qualification as described in the video below if they wish to continue working as electricians.

 
When protection of title is eventually introduced it will apply only to electricians who are based in Scotland. My information is that a database containing the details of all registered electricians in Scotland will be built and be administered by SELECT, NICEIC and the SJIB. NICEIC were initially opposed to the proposal but are now fully on board. Only those electricians who hold appropriate, up to date qualifications will be eligible for inclusion on the database. If your name isn't on the database and you as much as even advertise yourself as an electrician you will be committing a criminal offence. My understanding is that electricians whose qualifications are inadequate or have lapsed will be given a time-limited opportunity to get up to speed.

NICEIC Domestic Installers and those who have entered the industry via short courses will have to invest heavily to achieve the recognised level of qualification as described in the video below if they wish to continue working as electricians.

I'd give that an "informative" response if it was still about (@Dan ;)), but as it is you'll have to settle for a like :grin:
 
When protection of title is eventually introduced it will apply only to electricians who are based in Scotland.
Good luck then to those of you bssed a short drive from the border.
NICEIC Domestic Installers and those who have entered the industry via short courses will have to invest heavily to achieve the recognised level of qualification as described ...
Like I said, be careful what you wish for, you might get it :rolleyes: If that is the case then it'll create an instant shortage which you may think is a good thing - meaning you can put your rates up. But it'll also create an environment for chancers and BIY to thrive - which they will since there won't be the resources to enforce it in the same way that the police don't have the resources to deal with theives emptying your van.
 

Reply to Yet Another Dodgy EICR in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The buyer of my house has had an EICR done. I have anonymized and attached. Also the associated quote for remediation. I am wondering: surely...
Replies
26
Views
3K
I commissioned an EICR to be done on a property that is in Wales as this is now a requirement in order to let on any new tenancies after 1st...
Replies
1
Views
2K
Agent contacts me with an urgent request for a CU upgrade in Camden. They send over an EICR done the previous month and I have a quick skim. All...
Replies
99
Views
10K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Next door neighbour .Single mother 2 young kids . Been there 6-7 years .landlady is super reluctant to ever communicate no matter what the issue ...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock