Discuss Ze and distance from substation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

ringer

-
Reaction score
116
Was shown a PIR by a friend today where the Ze was recorded as 0.01 ohms. Not unexpectedly, the PFC was sky high at 19.9kA. I have never come across a Ze so low before. This is commercial premises, with a single phase TN-S supply. Now the nearest substation I am aware of is 150m away as the crow flies, or 250m away by road, which is more likely to be the route of supply cable takes from the substation to the property. Does a Ze this low seem likely at such a distance?
 
Was it an actual proper reading.
It is the devils own job normally to get a situation in a commercial premises where you can isolate the entire supply and take a reading.
Some do arrange shutdowns and take a correct reading, some may take a reading when the installation is on just to prove a path and many others make it up as they go along.
 
To be honest TD it will very much depend on the protection device on the main incomer which could be a BS 88 fuse for commercial.

If there are distribution boards around then those PD will dpend very much on the Zdb at each board
 
I think as others have said, perhaps where you tested isn't the origin of the return path ?
Maybe some parallel paths reducing your figure?
Are you physically able to see the earth strap coming off the casing of the incomer and confirm this what you tested ?
 
Last edited by a moderator:
These measurements were made and recorded by someone else. I was just shown the PIR and had a quick look around. There are other issues with the PIR where recorded readings (or no readings were recorded!) do not ring true. Premises were in use at the time so was not possible to take my own readings. Hoping to get back soon when they are not open to do my own testing. I had remembered IQ's method for low values and intend to employ it. However I suspect that original reading for Ze was taken with bonding in place.

What I was asking originally was whether you might expect to get such a low Ze 250m away from the substation on a TN-S supply? The area is heavily built up with both commercial and residential premises.
 
If the standard of the paperwork is generally poor then I would wait to verify that Ze reading yourself before going too deep into the ramifications of it being so low. Could easily be a clerical error with a decimal point in the wrong place. My house is on TNS and has a Ze of 0.1.
Personally not had a reading as low as 0.01.
 
Site I work on has it's own TV network that is why they don't use MCBs specify that it has to be fuses.

Why's that then?? I know why to be honest, but that spec is based on cost effectiveness rather than anything else!! Having said that, HRC fuses can get mighty expensive, if you blow a few in the course of fault finding. Especially where some, will just replace the fuse without checking for a fault first etc... lol!!!

We use 22KA MCBs in a number of cases on our projects, in fact i can't remember the last time we have used fuses on the LV systems, can't say we use many fuses on the MV side of things either, apart from in the odd RMU and in the moving MV contact arms to voltage transformers in the main MV switchboards....
 

Reply to Ze and distance from substation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
Another long one from me ... I hope that it covers all the bases and is a more thorough approach to the subject. It is my first design work so...
Replies
44
Views
6K
G
Hi So today i tested at the orgin of the installation and on my MFT 1552 Megger, i got a reading of <0.01 for Ze and >19.9 KA for PFC, it's a...
Replies
6
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top