Discuss ze testing - high current or no trip in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

B

BES

Testing for cu change .Customer had eic for 2 wy rcd protected cu fitted for kitchen sockets when refurbed a year ago. no prob but noticed the ze had been put down as 0.41(tncs) bit high so i tested on high current as always 0.21 changed to no trip 0.42. ive never test ze on no trip as high current gives a more accurate value.
i just wondered what setting others use when testing ze.
cheers
neil
 
Not sure why you'd want to test Ze on no-trip loop setting. Doesn't make a lot of sense.

But I agree with you that non-trip loop can give sky-high readings at times.
 
Exactly i can only think that the person who took the reading for kitchen refurb must have had his tester on no trip as when i took measurement on no trip it was 0.42 approx the same. Wouldnt you query this if you got. Such a reading on a tncs. As well as that the value of main fuse was incorrect and all the schedule of inspection items were tick including selv/pelv not a 12v in the house and some items u wouldnt except to be applicale in domestic. This was filled in by a niceic fully approved company looks like the certs were filled in before job was done
 
Last edited by a moderator:
Ze can never need the no trip setting, though I did not realise it could make such a difference, I thought it was just a little bit high.
I would only do it If I was rechecking later and forgot to change the setting!
 
exactly the reason i asked queston was result on eic for kitchen obviously person who tested it stll had tester on no trp when checking ze but wouldnt you realse something bt odd with ze being 0.41 on a tncs and also the pfc on eic was 1.1ka a result you would get from a much lower reading of ze. just thought i was a along with the other mistakes on cert is a bit poor.
 
Last edited by a moderator:

Reply to ze testing - high current or no trip in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
So a customer had a nuisance trip and I spent 4 hours trying to find the fault (first hour identifying circuits as none labelled at board). There...
Replies
18
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Evening all. I did an EICR recently and then changed a consumer unit. As part of the EICR process I take off around 25% of all accessories to...
Replies
9
Views
2K
I’d like your opinions on a scenario I’ve come across. A certificate was produced which contained errors and while there were still faults on the...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock