As a guide in the 17th the max Ze readings for the following =
Tns = 0.8
Tncs = 0.35
TT = 200
I Recently got a Ze reading of 0.15 on a Tns system, as its higher than 0.8 in the 17th should i be worried?
If its ok, what Ze readings would you consider high for each of the systems? e.g time to call the DNO.
Also filling out a certificate with a higher Ze reading than recommended in bs7671, allowed?
Tns = 0.8
Tncs = 0.35
TT = 200
I Recently got a Ze reading of 0.15 on a Tns system, as its higher than 0.8 in the 17th should i be worried?
If its ok, what Ze readings would you consider high for each of the systems? e.g time to call the DNO.
Also filling out a certificate with a higher Ze reading than recommended in bs7671, allowed?