As a guide in the 17th the max Ze readings for the following =
Tns = 0.8
Tncs = 0.35
TT = 200

I Recently got a Ze reading of 0.15 on a Tns system, as its higher than 0.8 in the 17th should i be worried?
If its ok, what Ze readings would you consider high for each of the systems? e.g time to call the DNO.
Also filling out a certificate with a higher Ze reading than recommended in bs7671, allowed?
 
As a guide in the 17th the max Ze readings for the following =
Tns = 0.8
Tncs = 0.35
TT = 200

I Recently got a Ze reading of 0.15 on a Tns system, as its higher than 0.8 in the 17th should i be worried?
If its ok, what Ze readings would you consider high for each of the systems? e.g time to call the DNO.
Also filling out a certificate with a higher Ze reading than recommended in bs7671, allowed?
with maths like that, you'll never make a scouse wheel thief. you'd nick1 and say it was more than 4!
 
Give the OP a break, most prob a brain fart moment....
 
Good grief!

Where exactly on BS7671 did you get that lot from?

There is no guideline maximum for Ze on a TT system, and if there was it's hardly going to be 200ohms is it!
Oh and 80 is higher than 15!
 
As a guide in the 17th the max Ze readings for the following =
Tns = 0.8
Tncs = 0.35
TT = 200

I Recently got a Ze reading of 0.15 on a Tns system, as its higher than 0.8 in the 17th should i be worried?
If its ok, what Ze readings would you consider high for each of the systems? e.g time to call the DNO.
Also filling out a certificate with a higher Ze reading than recommended in bs7671, allowed?

Stop making out that scousers are thick
 
Hi,dude, You will have to grow a sense of humour,as you have only had 20% of the 100% normally given,which is,after all,only one seventh....:conehead:
 
0.80 implies greater accuracy than value than 0.8

Could it be that it was 0.8 exactly, with the zero dropped as it would be irrelevant, to the outcome calcs.
Sorry I'm trying to get my head around this, not disrespecting your post.
 
Could it be that it was 0.8 exactly, with the zero dropped as it would be irrelevant, to the outcome calcs.
Sorry I'm trying to get my head around this, not disrespecting your post.

The zero is relevant to the outcome of the calculation as it will have an impact on its accuracy.
0.8 x 0.320 = 0.3
0.80 x 0.320 = 0.26
0.800 x 0.320 = 0.256

0.8 is a value anywhere between 0.75 and 0.84 wheras 0.80 is a value between 0.795 and 0.804
 
The zero is relevant to the outcome of the calculation as it will have an impact on its accuracy.
0.8 x 0.320 = 0.3
0.80 x 0.320 = 0.26
0.800 x 0.320 = 0.256

0.8 is a value anywhere between 0.75 and 0.84 wheras 0.80 is a value between 0.795 and 0.804

...Your calculator needs re-calibrating...:icon12:
 
Could it be that it was 0.8 exactly, with the zero dropped as it would be irrelevant, to the outcome calcs.
Sorry I'm trying to get my head around this, not disrespecting your post.

Yes mate. If the 2nd, 3rd 4th etc decimal place is not required, dont need to use it or it would become 0.800000 or 0.8 X 10 to the power of minus 6 :wink: (level 3 maths, you will see)

^^ that is correct isn't it gents? Been a long time since writing this form of equation and it does not look right?
 
This is getting too in depth,anyone know if my maths are right,I seem to keep getting e=mc squared
icon11.png
 
Yes mate. If the 2nd, 3rd 4th etc decimal place is not required, dont need to use it or it would become 0.800000 or 0.8 X 10 to the power of minus 6 :wink: (level 3 maths, you will see)

^^ that is correct isn't it gents? Been a long time since writing this form of equation and it does not look right?

Yes you do, the number of decimal places displayed is significant in any calculation as it defines the accuracy of the end result. There's no point using a good quality tester which reads to 2dp then only recording the result to 1dp, you might as well use a less accurate tester.

Oh and 0.8 x 10 to the -6 would be 0.000008 ;)

(Or it might even be 0.00000008, thanks Mr styrofoam)
 
Last edited:
...This is why that Mars lander bounced off in to the yonder....

"By calculation", 0.8 x 0.320 = 0.256 not 0.3

By restraint of scale,rounding down etc,yes,but NOT by calculation,which by its' description,is definitive.

0.8 x 10 to the -6 is 0.0000008 or 8 to the -7 , the power of -6 being a millionth,micro or multiple of 0.000001.

...And,as my maths teacher was inclined to ask,after a grueling,set of calcs,"We know friction makes heat?...and heat boils water?...So how long will it take a donkey to ---- a bucket of water,so we can have a cup of tea?" :icon12:
 
...This is why that Mars lander bounced off in to the yonder....

"By calculation", 0.8 x 0.320 = 0.256 not 0.3

By restraint of scale,rounding down etc,yes,but NOT by calculation,which by its' description,is definitive.

0.8 x 10 to the -6 is 0.0000008 or 8 to the -7 , the power of -6 being a millionth,micro or multiple of 0.000001.

...And,as my maths teacher was inclined to ask,after a grueling,set of calcs,"We know friction makes heat?...and heat boils water?...So how long will it take a donkey to ---- a bucket of water,so we can have a cup of tea?" :icon12:

about 15 minutes if the donkey's on ------,
 
Ok I should have said 0.8ohms x 0.320 =0.256

In any scientific calculation an answer cannot be more accurate than the least accurate input value.

Indeed, but you shouldn't make any assumptions about accuracy based only on the number of decimal places or significant figures used.

See my post here: http://www.electriciansforums.co.uk...0424-three-phase-calculation.html#post1079853

My multimeter shows values to 4 significant figures. Can I assume that it's accurate to plus/minus half of the final digit? No! But I still might write down the value I see on the display.

Here's another (silly) example: Would a shop selling something for £1.49 accept a "one pound" coin (0 decimal places), since it's not labelled as a "£1.00" coin?
 
Indeed, but you shouldn't make any assumptions about accuracy based only on the number of decimal places or significant figures used.

See my post here: http://www.electriciansforums.co.uk...0424-three-phase-calculation.html#post1079853

My multimeter shows values to 4 significant figures. Can I assume that it's accurate to plus/minus half of the final digit? No! But I still might write down the value I see on the display.

Here's another (silly) example: Would a shop selling something for £1.49 accept a "one pound" coin (0 decimal places), since it's not labelled as a "£1.00" coin?

Around about now my dear old physics teacher would be tearing a few strips off you!
 
The zero is relevant to the outcome of the calculation as it will have an impact on its accuracy.
0.8 x 0.320 = 0.3
0.80 x 0.320 = 0.26
0.800 x 0.320 = 0.256

0.8 is a value anywhere between 0.75 and 0.84 wheras 0.80 is a value between 0.795 and 0.804

Thanks for replying - it's appreciated, I'm a bit confused cos my calcs show the number of zeros is irrelevant.
I suspect it's expressed as 0.8 because that's what it is. If it was 0.802 then this would have to be noted
that 0.8 is correct to x decimal places. ??

0.8x 0.320 = 0.256
0.80=0.320 = 0.256
0800x0.320 = 0.256
 

Reply to Ze Values? HELP in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
Replies
7
Views
953
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Cable calcs using cable calc app Working out cable size for a workshop. 100m long, 100a supply, mccb 100a zs- 0.23 ohms, in a duct on its own...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock