Discuss Zs measurements in the Cert column in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

cliffed

-
Arms
Supporter
Reaction score
649
Still having a discussion @ work about this…TNCS system DB/CU is a split 30ma RCD configuration,5/5
MCB’S are 60898 what Max Zs would you put in the column for Max measurement for the MCB😎
 
On a TN system I would normally base it on the MCB Zs value.

Yes, you can disconnect according to regs on 1667 ohms with 30mA RCD, but on TN-C-S it ought to be pretty low and unless it is an unusual situation, anything above the usual OSG sort of tabulated values suggests a fault in the circuit implementation which needs fixing, not a planned use of the RCD.

High current sub-main, or TT earthing, are a very different kettle of fish.
 
Last edited:

Reply to Zs measurements in the Cert column in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
848
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
497
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
1K
Hi, can someone give me some advice RE completing a small works certificate for a fused spur coming from a ring final. 1) In part 2 of the AMD2...
Replies
35
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock