Discuss Zs of circuit higher than maximum values allowed? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
13
Hi there,
I have a ring circuit where the Zs reading taken is higher than maximum allowed values.
the circuit is protected by a 32a RCBO type C device, Zs = 1.43.
I have currently have tightened terminations which has brought it to its current value.

as i have been out of the game for a while i wondered if the rcbo can overide maximum values is sufficient Zs is not achieved.

many thanks in advance!!
 
Even if you changed it to type B you would still be 0.33 ohms out or thereabouts. Why is it type C? What is the Ze and earthing arrangement? A possible solution may be splitting the RFC into two radials on 16/20A MCBs, depending on the R1R2s and consequent Zs's when the cct is split.

I personally would not be overly happy relying solely on the RCD for fault protection if there is a suitable work around. Better to have the RCD as additional protection.
 
I have come across this quite a lot even in new installation that have been designed using Type C RCBOs although Zs results have been more around 0.80 ohms an although as the Gay owl suggest its not a good idea just to relay on RCD protection to disconnect the supply in the event of a fault I have been guided if carrying out an ECIR to code 3 this is as long as the RCD is found to be operating corrrectly , It sound like the circuit in your case as been poorly designed and may have other issues such as a high volt drop so you may need to be looking at a 20 amp type B RCBO
 
You have to look at the design of the circuit and see if the values you have measured are in the right sort of range for that circuit.
If it is a ring circuit with only six sockets over a 10m ring then your Zs should be 0.05Ω greater than your Ze, but a 100m ring should be 0.5 plus your Ze, by pure calculation.
With all the connections and so on you can expect a reasonable variation from this but only by a few tenths of an ohm.
If your circuit should be OK then it is time to look for the fault, resistance in the RCBO, loose connections, etc.

If the ring has been installed such that the Zs would be exceeded by calculation then this is a badly designed ring and it would be preferred to resolve this bad design rather than relying on the RCD EFLI limits.
 
Hi guys thanks for your help and input.
I believe the circuit may be too long hence the values ill be in the apartment tommorow and will post end to ends of the ring.
so far i have only done calculated readings as i did a QA of the install before walls were put so have verified the ring visually.
What i will do is go around again tommorow and tighten all terminations as i believe i could do it better. the sockets are module type where you have to link out the modules so quite a few terminations. There are about 12 sockets on the ring including floor boxes. Hopefully i can get r1+r2 towards or beneth 1.20ohms which will allow a type B Rcbo provided i can get 1.80ohms or lower L-L and 3.00 ohms or lower cpc.
 
Last edited:
Or a carp Ze possibly.

Twelve sockets on a RFC is not that many, although there is a good few terminations as you say. Don't forget bonding will very likely bring the actual recorded Zs down lower. Need to get testing.
 
Take a Zs on the busbar terminal of RCBO and one on the L Load of RCBO and you will see what it is adding. If it is the unit adding it to your reading then make a note on cert and put 1667 as maximum Zs for that circuit only.
 

Reply to Zs of circuit higher than maximum values allowed? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
708
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
I would appreciate some opinions on the following situation... I have been asked to comment on an EICR for a local community resource (church hall...
Replies
14
Views
3K
Hello. So, I would like to know how I can choose the correct circuit breaker value when doing a new installation. My example is: I have 16...
Replies
2
Views
867

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock