Discuss zs problems in the UK Electrical Forum area at ElectriciansForums.net

B

bethelec

Any clues??? Trying to test zs at Lv panel incomer fed from transformer. With main switch turned on and feed to site temps (offices, 110v trannies etc) on I get a voltage between neutral and earth. With main switch off so feed goes from transformer to lv panel incomer only I get open reading. I have disconnected earth link on earth bar and taken out earth that feeds earth nest but still no reading. All cpc's are connected. Any advice or pointers would be grateful as I am stumped
 
You should not have any voltage between Neutral and Earth, they should be at the same potential.
If you have voltage between Neutral and Earth when the installation is on then this is indicative of a poor connection, usually of the neutral conductor, to the installation.
 
Much more information needed.

If this is the incoming from a DNO transformer you should not be removing the N→E link! I would only contemplate it if the transformer is isolated.
 

Reply to zs problems in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
482
Today I came across an earth cable from the earth bar in the DB that went directly into the incoming neutral side of the main switch. The DB is...
Replies
14
Views
2K
Been asked to do some rewiring, and have said needs upgrade of consumer unit really Main question is regarding earthing - Zs reads at 0.45 ohms...
Replies
7
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock