My instinct here will be to replace the MCB With a Rcbo, tell the Client a FI will be required,& appropriate tests to be made on that circuit.
At least for now an Earth fault will be protected by the Rcbo…..which will be better than it is now.
My attachment above states that reasoning too.
I cannot quite understand why a few of you disagree with that option…& I fully understand the short circuit requirements…& that is typically of the high Zs reading on circuits where the Zs are high.
My concerns will also be directed @ the Company I work for…
 
I have to agree that attempting to temporarily mitigate this CPC fault by installing an RCBO is not an acceptable approach.

The allowance in the regs for using an RCD as supplementary protection is a design consideration, not a fault correction provision.

If you had not been given time to locate and correct the fault, the circuit should have been disconnected as it is potentially dangerous.

At least that's the way I look at it...
 
My instinct here will be to replace the MCB With a Rcbo, tell the Client a FI will be required,& appropriate tests to be made on that circuit.
At least for now an Earth fault will be protected by the Rcbo…..which will be better than it is now.
My attachment above states that reasoning too.
I cannot quite understand why a few of you disagree with that option…& I fully understand the short circuit requirements…& that is typically of the high Zs reading on circuits where the Zs are high.
My concerns will also be directed @ the Company I work for…
It is you that doesn't understand. Further dead tests should have been undertaken to establish the issue. How do you know the rcbo will protect under earth fault conditions the earth may totally break down under fault.
 
I have to agree that attempting to temporarily mitigate this CPC fault by installing an RCBO is not an acceptable approach.

The allowance in the regs for using an RCD as supplementary protection is a design consideration, not a fault correction provision.

If you had not been given time to locate and correct the fault, the circuit should have been disconnected as it is potentially dangerous.

At least that's the way I look at it...
Agree… so what about the high loop impedances found on other citcuits that do not comply eg ring main circuits just stick a Rcbo on it…
 
When I have trainess/improvers working with me I always insist they work out the expected value of R1/R2 etc. Also for Ring Final Circuit tests, always calculate the expected value before measuring. So in the case above you would have an expected value derived from the estimated length of the circuit and so on. This would the verify if the circuit is too long of there a comparable value which can indicate a definite fault. I guess I would be out with the wander lead going light to light getting R2, or even between lights if the circuit is too long.
 
When I have trainess/improvers working with me I always insist they work out the expected value of R1/R2 etc. Also for Ring Final Circuit tests, always calculate the expected value before measuring. So in the case above you would have an expected value derived from the estimated length of the circuit and so on. This would the verify if the circuit is too long of there a comparable value which can indicate a definite fault. I guess I would be out with the wander lead going light to light getting R2, or even between lights if the circuit is too long.
Thanks
 

Reply to Zs reading high on external lighting in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
I've just finished an installation on a large outhouse around 50 meters from the main property, but I'm having issues with unusually high Zs...
Replies
11
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top