Discuss zs readings before and after rcd. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
2
anyone come across this before zs at board 0.28. then when measure zs on rcd side on live and neutral, reading of 0.77. from the same earth position.?, ie got a socket a meter away from board earth loop 0.81. measure earth from socket to board its 0.02.
 
that's nothing. i once has a RCD adding 149 ohms to the Zs. took me almost an hour to suss it out,
 
I'll think you'll find that this will be case with MK RCD's... got caught out this myself. EFLI testing on the supply side would give similar value to that of Ze but Zs was nearly 1 ohm.. turns out that the RCD was adding excess of 0.70-0.80 ohms.

It's a combination of RCD and testers no trip circuitry on my mft1552.

True Zs results can be calculated by subtracting the reading of the RCD input from the outputs and then subtracting that result from your sub circuit Zs.
 
I'll think you'll find that this will be case with MK RCD's... got caught out this myself. EFLI testing on the supply side would give similar value to that of Ze but Zs was nearly 1 ohm.. turns out that the RCD was adding excess of 0.70-0.80 ohms.

It's a combination of RCD and testers no trip circuitry on my mft1552.

True Zs results can be calculated by subtracting the reading of the RCD input from the outputs and then subtracting that result from your sub circuit Zs.
yes mine is the mft 1730 and mine is adding about .5/.6 ohms, just tried it at my house with a wylex rcd and getting about 0nly .1 ohm.
 

Reply to zs readings before and after rcd. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
666
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
342
Anyone come across this before? I was asked to do a Zs on a 3ph surge device; L1 was around 6 ohm, L2 & L3 around 0.11. Wired in singles from a...
Replies
1
Views
441
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
252

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock