Discuss Zs test furthest point ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

tank

-
Reaction score
16
hello all, could somebody clarify something for me, please, as there seems to be some disagreement among sparkies as to where the furthest point electrically in a lighting circuit actually is. this for a Zs test.

is it at the ceiling rose, as i thought, with switch closed, and probing switch live and cpc? this would appear to be the furthest point for the line conductor but not for the cpc which carries on the the switch plate.

the ceiling rose camp seems to be quite large.

but after staring at the Megger testing poster for the Zs test, ( they probe cpc and switch side of the switch), i now think this is correct. as we are testing for earth fault loop impedance anyway, surely it's proper that we test at the switch plate, as this would test a loop that incorporates all of the cpc. ( not just all of the line conductor , as with a ceiling rose test )

i'm new to testing, so i may be talking out of my hole, any thoughts?
 
highest Zs could be at either point depending how it is wired, especially if its a 2 way, the highest value is recorded anyway so test each point until you read highest reading. if you have an RCD on the circuit you would most likely need a neutral for triplock/ no trip depending on meter so would be tied again on the way the installation was wired ie loop in at rose or switch
 
Last edited by a moderator:
Anyone got the revelvant Guidance Note on testing to hand?

edit - Ok, just been to the office and its guidance note 3. A quick flick through shows pictures of the test being done at the switch.

I'm sure others will wade in with a better more comprehensive description!!
 
Last edited by a moderator:

Reply to Zs test furthest point ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi Im an apprentice and just wanted to clarify domestic style wiring since i work industrial and don't deal with conventional wiring. in college...
Replies
1
Views
918
Hi everyone, I really hope someone will be able to help. So last night I tried to change 2 ceiling rose / pendant lights at my mother in laws...
Replies
5
Views
1K
Hi guys, I have recently encountered that my circuit breaker for the upstairs lights keeps tripping. I flick it back on and immediately it trips...
Replies
7
Views
918
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
827
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock