Discuss Zs test tripping RCD. in the UK Electrical Forum area at ElectriciansForums.net

if your tester puts 15mA through for the test and there's inherent leakage of 8 -10 mA on the installation, it may well trip. do a ramp test first .
 
I've had this before, it was a 100mA main switch RCD, on 2 of the circuits cooker and ringmain, the RCD would trip on loop test l, turns out a screw was put through the cooker cable with a dead short on N-E, or try a Ramp test, and I take it your on No Trip mode, goodluck
 
Look on the plus side as well , now you've done the test with all circuits connected as well and found RCD trips , you now know theres a fault on one of the circuits or appliances , but as already said RCD tests are best done at the board as appliances such as fridges etc will give false readings anyway..

oops just re read the ops question , Zs testing not RCD ..still same applies ,
 
Last edited by a moderator:

Reply to Zs test tripping RCD. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
346
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
899
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
823
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
564

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock