Search the forum,

Discuss Zs values? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

B

bs7671

Hi there I have another question for you guys.What is the maximum Zs values for different circuit breakers i.e type B,C,D also where would we find them and why the difference?
 
the difference is due to the different characteristics of the breakers. the Zs max. is the max. you can allow for the particular breaker to disconnect in the permitted time
 
I want to find a table or something so I can see the Ka ratings as per different device type.Or at least someone to explain it in simpleton terms
 
It's the 'on no trip' bit that you need to question.

Most no-trip readings are much higher than conventional Zs readings using a full-current test.

There's also a chance that the RCD is distorting your reading.
 
I want to find a table or something so I can see the Ka ratings as per different device type.Or at least someone to explain it in simpleton terms
on site guide and GN3 have tables with the standard kA ratings of all protective devices manufactures will give more details
 
0.06 seems low to me for Ze. if i am doing Zs on no trip, i usually do the Ze on no trip . no doubt someone will correct me on this, but i do it this way so as to make the readings same parameters as regards the test equipment.
 
Last edited:
why are osg tables 80% of bs7671?

When you do the Zs test the cable temperature will be around 20°C. The tables in the regs are the max Zs values when the cable temperature is 70°C.

As resistance increases as cables get hotter (0.4% per °C) you need to adjust the max Zs value for the lower temperature of the cable.

e.g The difference between 20°C and 70°C is 50 so the calculation would be 50 x 0.4% = 20% so the corrected max Zs values for 20°C would be 20% less than the ones for 70°C.

Hope that makes sense ;)
 
malcolm, could you clarify your last post please. say for a 32AMCB, the max. allowable value of Zs is 1.16, what you are saying is, if the circuit is RCD protected you enter 1667, not 1.16?
 
so, one advantage of the 17th is, with everything now on RCD ( well almost), we don't have to remember all those max. Zsvalues for different MCBs. every cloud has a silver spoon!
 
RCD/RCBO circuits will have the Zs part of the form filled in as 1667 as that is the "Zs" as such for the circuit.

On domestic the chances are that as the board that is fitted will be a dual board then you also have overload protection by MCB and that circuit will have your Zs, and you will enter the Zs results. A lot of argument is now happening that even on dual boards you can fill the Zs for each circuit as 1667 as all circuits are RCD protected. IMO in a few years once we are all use to this we will all fill the schedule of resutls with RCD protection as 1667. I have to admit until recently I use to fill the Zs part in for each circuit as measured but I will start doing it the 1667 method.

Obviously on PIR's for older installtions, and installtions not needing RCD protection you will still do Zs as normal.
 
even so, still put in the measured Zs in it's column, but max. as 1667.
 
Well that's your answer Malcolm, the Lord hath spoken!

And on the seventh day, the NICEIC wrote the regulations!
 
1667 is for TT systems.
On a TNS system the mcb or rcbo is your method of complying with 411.3.2.2 & you use table 41.3
The rcd is for additional protection so 1667 does not come into it.

Table 41.5 is for TT systems.
 
1667 is for TT systems.
On a TNS system the mcb or rcbo is your method of complying with 411.3.2.2 & you use table 41.3
The rcd is for additional protection so 1667 does not come into it.

Table 41.5 is for TT systems.

If the maximum Zs value for a circuit in a TN system cannot be met, the circuit may be protected by a 30ma RCD. 531.3.1
 
Last edited:
A common source of misunderstanding is that of either specifying or measuring values of ELI where the circuit also has an RCD fitted. ELI measurement under these circumstances is a futile excercise.

The circuit will have been checked for continuity, and this is all that is needed together with, of course, functional checks of the RCD.
This criterion satisfies requirements for automatic disconnection.

The subject is somewhat confused by the inclusion of RCBO's in table 41.3 and for clarification, circuits with RCBO's do not need to meet the specified ELI values.
 
If the maximum Zs value for a circuit in a TN system cannot be met, the circuit may be protected by a 30ma RCD. 531.3.1

I'm not sure that you can use that in a domestic situation Sintra, 531.3.1 does not deal with circuits but equipment in certain parts of a circuit.
So if you have a high Zs on a final ring circuit for example, you cannot just use the rcd as your main protection in my opinion.
Though I am of course open to being shown otherwise.
 
Personally i don't see any reason not to as it has been done like this on a TT for years.
 
I'm not sure that you can use that in a domestic situation Sintra, 531.3.1 does not deal with circuits but equipment in certain parts of a circuit.
So if you have a high Zs on a final ring circuit for example, you cannot just use the rcd as your main protection in my opinion.
Though I am of course open to being shown otherwise.

well if you check on how to correct a High Zs reading there are 2 main options increase the size of your cpc or install and RCD , so in theory if you have an installation thats protected by an RCD you can have higher than the permitted Zs readings , i must admit i prefer to get the readings withing the permitted levels
 
i must admit i prefer to get the readings withing the permitted levels

Absolutely.

Unless it's a TT system there is no reason at all not to have Zs well within limits. A good design leads to a compliant install without the need for an RCD to cover a bad one.

The amount of times I've heard "dont worry about that there's an RCD on it anyway"
 
Last edited by a moderator:
So if you have a high Zs on a final ring circuit for example, you cannot just use the rcd as your main protection in my opinion.

You are correct regarding using the RCD as your main protection but with an RCBO, your overcurrent protection will be carried out by the 'O' part of the RCBO thereby satisfying the requirements for automatic disconnection.
 
Absolutely.

Unless it's a TT system there is no reason at all not to have Zs well within limits. A good design leads to a compliant install without the need for an RCD to cover a bad one.

The amount of times I've heard "dont worry about that there's an RCD on it anyway"

Agree with this also. On a new circuit it should never happen if designed correctly but it can be a quick fix on an existing circuit with a high Zs.
 
I'm getting confused (though let's face it , it doesn't take much). The table in the osg gives values for 60898 and 61009 which are mcb and rcbo. rcds without overcurrent protection are covered by 61008 so aren't included in this table I presume. If the table says it's the max value isn't that what I should be putting down?
 
I'm not sure that you can use that in a domestic situation Sintra, 531.3.1 does not deal with circuits but equipment in certain parts of a circuit.
So if you have a high Zs on a final ring circuit for example, you cannot just use the rcd as your main protection in my opinion.
Though I am of course open to being shown otherwise.

You are right, the RCD is not to be used as main protection. But when installing an RCD as regards to High Zs values it's classed as additional protection which is allowed.
Your main protection is still by ADS.
Personally I agree with Sinatra. A new installed circuit should nit be reading a high Zs. But, if I was coming across high readings on a PIR that where protected by an RCD I'd probably record the 1667 value.
 
Agree with this also. On a new circuit it should never happen if designed correctly but it can be a quick fix on an existing circuit with a high Zs.


Me to i recently did a rewire and due to restricted access cable runs were longer than id have liked and the calculated readings of 2 ring mains were a little higher than id have liked , so the rings were wired in 4mm twe instead of 2.5 , kept the readings low , it was a relativly small house but made of stone and a funny shape

oh and jeremy dont worry im always confused your not the only one
 
yes on tt system if ze less than 1667 then everythink ok.because rcd will disconnect in 0.2 thus satisfying 0.4 disconnection time
 
415.1.2

The use of RCD's is NOT recognised as a sole means of protection and does not obviate the need to apply one of the protective measures specified in sections 411 to 414.

To my mind that means getting your Zs and disconnection times within those specified irrespective of RCD's (TT's being the exception)
 
the maximum zs reading on a tn circuit incorporating an rcd shall be 1667 as per iee regs.therefore zs readings redundant on 99% of domestic installations
 
That's not said in the regs. Only regarding TT. But that is because on TT system you are going to get such variable readings from your earth rod they allow you to conform with formula
Ra In > 50v.
reversing the formula
50v/0.03mA= 1667 ohms. That the maximum Zs with an RCD that allows unto the safe touch voltage.
On a TN system you aren't going to get nowhere near that figure.
 

Reply to Zs values? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, I'm struggling with these questions for this circuit as the equations I have in order to work out impedance etc all seem to need the...
Replies
3
Views
265
Hi, I am currently reading through the standard IEC 61439-1 - Low-voltage swtichgear and controlgear assemblies - Part 1: General rules, and on...
Replies
0
Views
117
I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
859
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
2K
I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock