I understand how to test Ze and Zs and that Zs is the total impedance from the suppliers tranny to the final accessory in a circuit your testing. Also that Ze is the suppliers earth resistance.

However i have a few questions

1.) how does the test meter actually work to measure Ze by connecting the meter to the main earth (obviously main earth disconnected from MET) and to the phase conductor? does it link it out or send a current or what?

2.) Why and how does Zs effect a devices tripping time? like what is the theory behind it. I know Low Zs means that fault current will be higher thus tripping the device but how does it trip the device and what device MCB ? RCD? how does fault current going down earth trip a MCB?

3.) Would you be able to just do a test from the main isolator in the disboard and record that measurement for all the Zs readings (adding Ze reading off course) on different circuits or does it have to be done individually for each circuit to get the furthest point in the circuit?

4.)Does the meter measure prospective fault current by just using ohms law and dividing mains voltage by resistance of the cable but what i dont understand is how does the meter find the resistance of the cable does it pull a load on it and then calculate or what?


Thank you for your time
 
A few points Zs and ze are different reading , if you test at the mains as you say that will be ze ,you could link out a light (l-e)and test at the board but this would be a r1+r2 test witch is done dead not live . Efli testers don't trip mcbs they can trip rcds ,
 
A few points Zs and ze are different reading , if you test at the mains as you say that will be ze ,you could link out a light (l-e)and test at the board but this would be a r1+r2 test witch is done dead not live . Efli testers don't trip mcbs they can trip rcds ,
R1+R2. Big R not little r as this is end to ends.
 
basically your meter can only measure one thing.i.e.current. depending on what setting you are using, this current is converted by the meter into volts or ohms . think about a dead resistance measurement. the meter applies a voltage to the circuit (from it's batteries) and measures the current. this is translated into ohms by the mater using ohms law through it's internal electronics. when measuring Ze and Zs, the voltage is derived from the supply, not from the meter. this is why a separate EFLI tester does not have batteries.
 
There is ways round testing at the board on high current setting that bypasses the RCD tripping . Sure someone will be along soon who will post a diagram ( i cant seem to post pictures )
 
here:

High current Zs test with RCD.jpg
 
Mcbs work on thermal and magnetic principles. Magnetic for sudden rush of current like a short circuit which the thermal side will not sense quick enough. The thermal side is for overcurrent. The fault path will send current down the earth and line conductors and it is the line current which activates the device. Unless a device is faulty it is current only which activates a device or fuse.
 
Hi - I'll do an easy one :
4 - yes, if the meter is connected to measure Zs and then we flick to pfc, it is just using the rms voltage and applying Ohm's Law to give pfc.
 
I am still quite confused on why loop impedance has anything to do with how quick a protective device would trip? i just dont understand how earth has anything to do with a mcb tripping in short circuit conditions or the RCD tripping in earth fault conditions surely the RCD will see the difference in current regardless of the earth being high impedance or not?
 
A few points Zs and ze are different reading , if you test at the mains as you say that will be ze ,you could link out a light (l-e)and test at the board but this would be a r1+r2 test witch is done dead not live . Efli testers don't trip mcbs they can trip rcds ,
what confuses me is when i am always told Zs = Ze (R1+R2). so does that mean R1 and R2 is measured for each individual circuit by being cross connected then the ze measurement is added on that by the person testing to give Zs? so Zs is basically just R1 and R2 cross connected plus the Ze reading?

Its because i saw a video earlier showing a person testing Zs from a scoket outlet. but surely you can just test it like that because you would have to add the Ze reading?
 
what confuses me is when i am always told Zs = Ze (R1+R2). so does that mean R1 and R2 is measured for each individual circuit by being cross connected then the ze measurement is added on that by the tester to give Zs? so Zs is basically just R1 and R2 cross connected plus the Ze reading?
Meter sends a current 25amps through live and earth when meAsuring ze and records the volt drop and converts to ohms on the meter.
 
but why do you need to put a probe on the earth and the line conductor? does the meter short them out or something?
Hope not, there'd be a Big Bang :)
If we want to measure the resistance between two points we need to apply the test to those two points. Zs is between line and protective conductor, so leads are attached to line and protective conductor. Check 411.4.5 for definition. In terms of the meter that takes the measurement, it is a bit special as the circuit is live and in service. Not your average multimeter set on low Ohms range :)
 
Meter sends a current 25amps through live and earth when meAsuring ze and records the volt drop and converts to ohms on the meter.
but how can it record the volt drop when your not at the other end of the cable to measure the volt drop!!! does it magically go around the live and back through the earth?
 
Hope not, there'd be a Big Bang :)
If we want to measure the resistance between two points we need to apply the test to those two points. Zs is between line and protective conductor, so leads are attached to line and protective conductor. Check 411.4.5 for definition. In terms of the meter that makes is measurement, it is a bit special as the circuit is live and in service while the meter is taking this measurement. Not your average multimeter set on low Ohms range :)
but this is the concept i am struggling with you cannot measure the resistance of one piece of wire unless you have long leads either end or unless of course you cross connect and measure at end point?! thats why i am wondering how the meter does it for Ze
 

Reply to Zs, Ze how the tester works? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
279
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
483
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
887
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock