Understand the principles of circuit protection and don't lose too much sleep over the operation of an earth fault loop impedance tester, I commend you for wanting to know but it is clouding over what you NEED to know. Trust me it doesn't matter how it works.
 
but how can it record the volt drop when your not at the other end of the cable to measure the volt drop!!! does it magically go around the live and back through the earth?
In simple terms, the impedance of the phase-to-earth loop is measured by connecting a resistor (typically 10 Ohms) from the phase to the protective conductor as A fault current, usually something over 20 A, circulates in the fault loop, and the impedance of the loop is calculated within the instrument by dividing supply voltage by the value of this current. The resistance of the added resistor must be subtracted from this calculated value before the result is displayed. An alternative method is to measure the supply voltage both before and whilst the loop current is flowing. The difference is the volt drop in the loop due to the current, and loop impedance is calculated from voltage difference divided by current.
 
In simple terms, the impedance of the phase-to-earth loop is measured by connecting a resistor (typically 10 Ohms) from the phase to the protective conductor as A fault current, usually something over 20 A, circulates in the fault loop, and the impedance of the loop is calculated within the instrument by dividing supply voltage by the value of this current. The resistance of the added resistor must be subtracted from this calculated value before the result is displayed. An alternative method is to measure the supply voltage both before and whilst the loop current is flowing. The difference is the volt drop in the loop due to the current, and loop impedance is calculated from voltage difference divided by current.
THANK YOU!! now that has made a switch flick in my head, just a one more thing if you can how does Zs effect the tripping time of a MCB or RCD?
 
but this is the concept i am struggling with you cannot measure the resistance of one piece of wire unless you have long leads either end or unless of course you cross connect and measure at end point?! thats why i am wondering how the meter does it for Ze
Ahh - the missing piece for you may be - the line and the protective conductors ARE linked by the supplying transformer secondary winding. That is the circuit you are measuring. Does that help?
 
Ahh - the missing piece for you may be - the line and the protective conductors ARE linked by the supplying transformer secondary winding. That is the circuit you are measuring. Does that help?
THANKS! believe me that was a missing piece mate now it really is coming together its just sometimes at college they dont clarify things like this and it keeps you wondering. Just thinking of it now that piece of information you just said clarifys alot of other things. Thanks alot
 
Look in your post you have asked why a efli tester would trip a rcd , that each circuit is cross connectied for R1+R2 test and that you seen a video of some one pluging a tester in and if you add ze on to that value . That's why i thought you where either a diyer who has read this forum and picked up some of the terms or was a spark taking the Mick but if your doing you AM2 soon best of luck
 
Look in your post you have asked why a efli tester would trip a rcd , that each circuit is cross connectied for R1+R2 test and that you seen a video of some one pluging a tester in and if you add ze on to that value . That's why i thought you where either a diyer who has read this forum and picked up some of the terms or was a spark taking the Mick but if your doing you AM2 soon best of luck
No problem mate thanks for the info anyway. I think there may be a misunderstanding i was asking why Zs has anything to do with how fast a RCD trips in fault conditions
 
THANKS! believe me that was a missing piece mate now it really is coming together its just sometimes at college they dont clarify things like this and it keeps you wondering. Just thinking of it now that piece of information you just said clarifys alot of other things. Thanks alot
No worries, I've had plenty of wtf moments myself :)
 
Not buying it
Mate i am not selling anything honestly. I am asking this question seriosuly whats so hard to get? i have been told so many times you need low zs readings to achieve the correct disconnection times but i have never been told why and how Zs effects the disconnection times. I dont know if i come across as a wind up but honestly not/
 
THANK YOU!! now that has made a switch flick in my head, just a one more thing if you can how does Zs effect the tripping time of a MCB or RCD?
Take a 32 amp type b mcb max zs is 1.37 ohms.
Tripping time between 0.1-5 seconds is 5x the rated current of the mcb so 5x 32amp type b is 160 amps.
230v x cmin 0.95= 218.5 volts.
218.5 volts / 160amps gives you 1.37 ohms.
Basically whatever mcb type b device you have multiply it by 5 so 6amp mcb x6 = 30 amps.
218.5/30 amp = 7.28 ohms max zs.
Type c mcbs are multiplied by 10x rated current
Type D by 20x rated current.
aslong as your zs values are within their max values you will have compliance by ADS including any equipotential bonding conductors required
 
Take a 32 amp type b mcb max zs is 1.37 ohms.
Tripping time between 0.1-5 seconds is 5x the rated current of the mcb so 5x 32amp type b is 160 amps.
230v x cmin 0.95= 218.5 volts.
218.5 volts / 160amps gives you 1.37 ohms.
Basically whatever mcb type b device you have multiply it by 5 so 6amp mcb x6 = 30 amps.
218.5/30 amp = 7.28 ohms max zs.
Type c mcbs are multiplied by 10x rated current
Type D by 20x rated current.
aslong as your zs values are within their max values you will have compliance by ADS including any equipotential bonding conductors required
A max zs value for a 30mA rcd used for fault protection will be 1667 ohms as 50volts touch voltage /0.03 amps = 1667 ohms.
 
Take a 32 amp type b mcb max zs is 1.37 ohms.
Tripping time between 0.1-5 seconds is 5x the rated current of the mcb so 5x 32amp type b is 160 amps.
230v x cmin 0.95= 218.5 volts.
218.5 volts / 160amps gives you 1.37 ohms.
Basically whatever mcb type b device you have multiply it by 5 so 6amp mcb x6 = 30 amps.
218.5/30 amp = 7.28 ohms max zs.
Type c mcbs are multiplied by 10x rated current
Type D by 20x rated current.
aslong as your zs values are within their max values you will have compliance by ADS including any equipotential bonding conductors required
I see, I think the problem i was having was i was thinking of Zs as some sort of special test when its actually just the line and cpc conductors resitstance combined with the external earth, you mentioned ADS? what is that?
 
I see, I think the problem i was having was i was thinking of Zs as some sort of special test when its actually just the line and cpc conductors resitstance combined with the external earth, you mentioned ADS? what is that?
ADS is automatic disconnection of supply.
It's the mcb tripping under fault conditions
 
9
Mate i am not selling anything honestly. I am asking this question seriosuly whats so hard to get? i have been told so many times you need low zs readings to achieve the correct disconnection times but i have never been told why and how Zs effects the disconnection times. I dont know if i come across as a wind up but honestly not/
firstly MCB and rcd do different jobs ,so if you asking about tripping RCDs when doing efli tests that cool or if you asking why we have maximum zs for tripping times that fine too , it just your overloading your self with questions and adding them together so it doesn't make sense when your responding , if we got off on the wrong foot sorry ,i always said i wouldnt do the "get a electrian in , that under part P etc response s so it my bad
 

Reply to Zs, Ze how the tester works? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
289
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
486
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
896
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock