Discuss Zs in the UK Electrical Forum area at ElectriciansForums.net

cliffed

-
Arms
Supporter
Reaction score
645
Recently been to test new build,everything fine except for one area,lighting circuit should be reasonably low reading,like other circuits,but Zs is 2.20 ohms,other reading much lower,.66 ohms,1.2 ohms.This is a new build ,& would expect lower,at this stage, I'm just testing,would you be prepared to be happy on this reading.All protected by rcbo's 30 ma 10 amp.
 
what's your R1+R2? for the lighting and your Ze? could just be a long cable run.
 
Recently been to test new build,everything fine except for one area,lighting circuit should be reasonably low reading,like other circuits,but Zs is 2.20 ohms,other reading much lower,.66 ohms,1.2 ohms.This is a new build ,& would expect lower,at this stage, I'm just testing,would you be prepared to be happy on this reading.All protected by rcbo's 30 ma 10 amp.
BS and type of rcbo?
 
Recently been to test new build,everything fine except for one area,lighting circuit should be reasonably low reading,like other circuits,but Zs is 2.20 ohms,other reading much lower,.66 ohms,1.2 ohms.This is a new build ,& would expect lower,at this stage, I'm just testing,would you be prepared to be happy on this reading.All protected by rcbo's 30 ma 10 amp.

Swap the 2 lighting circuits between the RCBO's and see if the "variance" moves with them or not. RCD's and RCBO's can do odd things to Zs readings.....
 
R1+R2 works out about right then for the estimated length of circuit. All other circuits are giving readings that are expected and your confident the RCBO's tight on the busbar and the line conductors in the RCBO terminal tight with no trapped insulation then it can only be the RCBO. I would probably swap it for a 6A C type or 10A B type depending on the characteristics of the load. As it stands ATM the circuit still comply as the RCD part of the RCBO is providing fault protection.
 
R1+R2 works out about right then for the estimated length of circuit. All other circuits are giving readings that are expected and your confident the RCBO's tight on the busbar and the line conductors in the RCBO terminal tight with no trapped insulation then it can only be the RCBO. I would probably swap it for a 6A C type or 10A B type depending on the characteristics of the load. As it stands ATM the circuit still comply as the RCD part of the RCBO is providing fault protection.
Thanks,yes my thinking too,6 amp rcbo's,in place of 10 amp.
lenght of cable estimated by measuring.
 
Just swap the RCBO for one that is known to be fine and test again, start by eliminating the simple things. As Lee said if everything else tests out fine then maybe the RCBO is suspect.
 

Reply to Zs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
479

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock