You really need to focus on the length of SWA in question. If it was me I would completely strip down all the terminations BOTH ends and also IR from both ends at 500V minimum.
Ze at origin is a good reading
The 24 HR supply (general domestic) should going over to off peak too , you say to separate meters lmo check with your energy supplier that is the case else or would mean 2 element tank and 2 circuits one off peak one 24 HR (general domestic)
So do you have a dedicated off peak consumer unit and a 24 hour consumer unit , another question is the hw element long top entry. Just to add the whole supply goes over to off peak so you could switch the circuit over to 24 HR supply and have it on a time clock that way you could top up if need be.
He done well pulling them singles through back to the board.
Flexi conduit to new socket position very good in the circumstances. I hate conduit alterations, with the new conlok couplers could of carried on in steel conduit to new socket.
You could run a three core&earth from the nearest two way position make that your intermediate then what was the common wire join it up in the back of the box with the spare core in a connector/wago and at the new switch end strappers in L1 L2 common in common.
does not help the circuits in one...