  1. C

    This cannot be right! 0.8amp in N and 0amp in L

    I like this suggestion, thanks. will do it!
  2. C

    This cannot be right! 0.8amp in N and 0amp in L

    Found the faults. First one was a neutral wire worked free and contacted the metal casing of ceiling lights. 2nd fault was actually in a ring circuit. An appliance fault must have been the reason why the earth conductor melted through the cable contacting the neutral line. Now I need to...
  3. C

    I Need Work Looking for Electrical Labourer/Mate Work in London

    That's great thank you for contacting me. I am currently up north wiring up a chicken farm and hope to get something in London asap. I will contact you on your website .
  4. C

    This cannot be right! 0.8amp in N and 0amp in L

    the ohm meter measured about 6 ohms between earth and neutral, which suggests that it is metal touching metal somewhere along the circuit.
  5. C

    This cannot be right! 0.8amp in N and 0amp in L

    yes that is true, and i got a figure of approximately .8 amps 0.6 amps on the downstairs lighting circuit and 0.2 amps on the upstairs lighting circuit.
  6. C

    This cannot be right! 0.8amp in N and 0amp in L

    unfortunately i never got round to finding the location of the fault,the landlord was funny and did not want to give access and i have been called to another contract. what started the whole thing, was that the bathroom lighting circuit was not protected by RCD. when the circuit was put on an...
  7. C

    This cannot be right! 0.8amp in N and 0amp in L

    Traced the problem down to both the upstairs and down stairs lighting circuits. When disconnected neutral on these circuits the current meter fell to virtually zero amps. Measured the resistance between neutral and earth conductors and got approx 6 ohms. If there is a difference in voltage...
  8. C

    This cannot be right! 0.8amp in N and 0amp in L

    Traced the problem down to both the upstairs and down stairs lighting circuits. When disconnected neutral on these circuits the current meter fell to virtually zero amps. Measured the resistance between neutral and earth conductors and got approx 6 ohms. If there is a difference in voltage...
  9. C

    This cannot be right! 0.8amp in N and 0amp in L

    Thanks for the helpful suggestions folks. These all seem like possible reasons and nothing to do with insanity. I will proceed to isolate the right circuit tomorrow and do the insulation and polarity/wiring checks . Will let you know the outcome.
  10. C

    This cannot be right! 0.8amp in N and 0amp in L

    The lighting circuit needs rcd and since the Consumer unit is damaged and dangerous it was best to change the whole consumer unit. So before powering down and ripping out the old CU. some basic tests to ensure there was no leakage that may trip the rcd and therefore delay outage in the...
  11. C

    This cannot be right! 0.8amp in N and 0amp in L

    It's a TNS supply. Yeah I will try ripping out the neutrals to see which circuit to troubleshoot. The house is lived in and I do not have keys to access rooms to do insulation tests as the moment. But will get round to it once I identified which circuit
  12. C

    This cannot be right! 0.8amp in N and 0amp in L

    Hi all, This is really concerning. Turned off all breakers in a domestic single phase consumer unit. With just the main switch on I measure a 0.8 amp current in the neutral tail into the consumer unit and virtually zero current in the Live tail. This is using a clamp meter. One of the...
  13. C

    Electrician Jobs Electricians Mate Needed Kent Area

    They say Orpington is in kent, so yeah. Places such as sevenoaks are within reach, i have transport too.
  14. C

    Hello All

    thank you, i am told that the majority of those who jump ship to become electricians are demoralised IT support staff.
  15. C

    Electrician Jobs Electricians Mate Needed Kent Area

    Hello, do you still need assistance, I am available on weekdays. I have transport, and handtools and can start immediately. Done my 17th edition, C&G Initial verification, test and inspection. and a C&G course of domestic installation.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock