Apologies I did not mention that in my original post. It was the VAT on the materials that he wanted sorting out. I also mentioned offering labour only but he wants me to provide one cost which includes labour and materials.
I take on board what everyone has said and I am trying to get...
The builder is vat registered so he's saying I need to be unfortunately.
I have not checked the t&cs but I assume they would not approve. Iam not approaching any of their clients (it's a friend of the family) so I don't see why it's that bad. If all went well I would go full time on my own...
Hi there,
I have a question which I'm struggling to get an answer. I have spoken with 2 accountants but both of them want me to sign up with them for £40 a month before they will tell me what is the best approach.
I am currently employed and take home 44k PAYE. I have been doing some labour...
Its a 4 core swa on an old concrete warehouse. So I just though it would be a good idea to throw a separate earth. Just oit of interest how do I calculate the swa armouring? Is there a table?
Thanks for the replies. As the cable run is so far they're wanting to install a 63 amp supply which will leave some room for future installs.
So just for future reference when installing a sub main, do I calculate at the protective device size?
Im also looking to install a separate earth cable.
Hi there,
Just after some advice for a submain/DB I’m quoting. A client has asked for a 12way TP board to be installed in a warehouse and the length of run is 150 meters.
Section panel I’m coming from has a ZE of 0.05.
MCCB will be a Square D CDAE 63A so max zs 0.68 at 5 second.
Here’s my...
Thanks for the reply, after alot of googling and swearing I managed to crack it.
If it helps anyone the full set is here:
TinyUpload.com - best file hosting solution, with no limits, totaly free - http://s000.tinyupload.com/index.php?file_id=84863374538197611061
Hi there,
I've been trying to get my head around AutoCAD for a while now and I'm trying to produce a full template that has all the blocks and title pages needed for an electrical installations. I've now got all the blocks I need but I'm having problems setting up the dynamic blocks. Does...
Hi I've a few questions regarding volt drop. Apologies if its a little longwinded but I'd like to get my head around everything.
An example scenario is a section board with a TP sub main to lighting and power board (DB2)
Calculations for circuit :
Supply Voltage = 400 Volts
Ib - Design...
Thats a fair point.
So if I went for a 50mm:
mV/A/m 0.93 for 230v
Voltdrop = (mV/A/m x Length x Design current) / 1000
Voltdrop = ( 0.93 x 75 x 100 ) / 1000
Voltdrop = 6.98 Volts
Which gives some breathing space.
So is this correct to use the 230V values?
Are the 400v values only used on...
Hi I've got a question regarding volt drop.
When calculating volt drop to a 3 phase distribution board do I use 230v (11.5v) or 400v (20v)
The board I'm attempting to put a cable to is 75 meters away.
Design current 100A
From TABLE 4D4A Cable selected = 25 mm²
For 25 mm²: mV/A/m 1.75 for 230v...
Sorry for being a bit brief on my initial post, it was all I could remember.
The system was just a crazy rig up with twist connections everywhere!
After ripping it to bits and testing as suggested, it turned out to be the input aux cable that was faulty! Doh!
I didn't check it because the amp...