  4. L

    Cable Calculation Question

    Its a 4 core swa on an old concrete warehouse. So I just though it would be a good idea to throw a separate earth. Just oit of interest how do I calculate the swa armouring? Is there a table?
  5. L

    Cable Calculation Question

    Thanks for the replies. As the cable run is so far they're wanting to install a 63 amp supply which will leave some room for future installs. So just for future reference when installing a sub main, do I calculate at the protective device size? Im also looking to install a separate earth cable.
  6. L

    Cable Calculation Question

    Hi there, Just after some advice for a submain/DB I’m quoting. A client has asked for a 12way TP board to be installed in a warehouse and the length of run is 150 meters. Section panel I’m coming from has a ZE of 0.05. MCCB will be a Square D CDAE 63A so max zs 0.68 at 5 second. Here’s my...
  7. L

    AutoCAD

    Thanks for the reply, after alot of googling and swearing I managed to crack it. If it helps anyone the full set is here: TinyUpload.com - best file hosting solution, with no limits, totaly free - http://s000.tinyupload.com/index.php?file_id=84863374538197611061
  8. L

    AutoCAD

    Hi there, I've been trying to get my head around AutoCAD for a while now and I'm trying to produce a full template that has all the blocks and title pages needed for an electrical installations. I've now got all the blocks I need but I'm having problems setting up the dynamic blocks. Does...
  9. L

    Volt drop

    Hi I've a few questions regarding volt drop. Apologies if its a little longwinded but I'd like to get my head around everything. An example scenario is a section board with a TP sub main to lighting and power board (DB2) Calculations for circuit : Supply Voltage = 400 Volts Ib - Design...
  10. L

    Volt drop question

    That makes sense, cheers for clearing things up
  11. L

    Volt drop question

    Thats a fair point. So if I went for a 50mm: mV/A/m 0.93 for 230v Voltdrop = (mV/A/m x Length x Design current) / 1000 Voltdrop = ( 0.93 x 75 x 100 ) / 1000 Voltdrop = 6.98 Volts Which gives some breathing space. So is this correct to use the 230V values? Are the 400v values only used on...
  12. L

    Volt drop question

    Hi I've got a question regarding volt drop. When calculating volt drop to a 3 phase distribution board do I use 230v (11.5v) or 400v (20v) The board I'm attempting to put a cable to is 75 meters away. Design current 100A From TABLE 4D4A Cable selected = 25 mm² For 25 mm²: mV/A/m 1.75 for 230v...
  13. L

    Design software

    Cable-Mate Cable mate. Does the job for me and its a steal at £16
  14. L

    PA question

    Sorry for being a bit brief on my initial post, it was all I could remember. The system was just a crazy rig up with twist connections everywhere! After ripping it to bits and testing as suggested, it turned out to be the input aux cable that was faulty! Doh! I didn't check it because the amp...
  15. L

    PA question

    cheers for the info! I'm not to sure about the amps power rating. Didnt manage to find any markings on the amp

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock